I have bought a Victron Multiplus II 48/5000 (5000kW), and now I am looking at accessories for it.
One thing I'm failing to understand is why they recommend 70mm2 DC cabling?
It charges at max 70A (battery charge current), and inverts at max 4000W max. 4000W, let's say with 10% inefficiency, is 4400W. With a 48V battery that's around 92A. Let's say 100A.
Cable current rating depends on insulation, etc, but 25mm2 (4 AWG) wires are often rated at 150A or more (some much more), with a resistance of ~0.8 ohms/km. For 1m, cabling, that's about 0.08V voltage drop at 100A, which is about 0.2% loss.
Now maybe 25mm2 is a bit marginal, but surely 35mm2 would be enough? Why would they recommend 70mm2 which seems comically large?
One thing I'm failing to understand is why they recommend 70mm2 DC cabling?
It charges at max 70A (battery charge current), and inverts at max 4000W max. 4000W, let's say with 10% inefficiency, is 4400W. With a 48V battery that's around 92A. Let's say 100A.
Cable current rating depends on insulation, etc, but 25mm2 (4 AWG) wires are often rated at 150A or more (some much more), with a resistance of ~0.8 ohms/km. For 1m, cabling, that's about 0.08V voltage drop at 100A, which is about 0.2% loss.
Now maybe 25mm2 is a bit marginal, but surely 35mm2 would be enough? Why would they recommend 70mm2 which seems comically large?