Why exactly 2 AWG vs an 4 AWG? 2000W should have a max pull of 83.3A on a 24V system (not taking in account for surge). 4 AWG can handle 95A. Is it just because it doesn't meet the 1.2 to 1.25 overage for circuit ratings?MPPT to battery should be 8AWG
Battery to inverter should be 2AWG at least, 1AWG would be better.
Fuses look OK and I've got no complaints on the breaker as long as you use a decent quality breaker and not go super cheap. I've been happy with my T-Tocas breakers, have even tripped a couple a couple times on accident and they worked fine.
Because I'm on about 2 hours of sleep and mathed for 12v. ?Why exactly 2 AWG vs an 4 AWG? 2000W should have a max pull of 83.3A on a 24V system (not taking in account for surge). 4 AWG can handle 95A. Is it just because it doesn't meet the 1.2 to 1.25 overage for circuit ratings?
Thank you for the explanation. Do you have a source or is this just a tribal knowledge thing? Not questioning, just wanna see what other stuff I can learn as well.2000 ac watts / .85 conversion factor / 20 volts low cutoff = 117.647058824 inverter amps
117.647058824 inverter amps / .8 fuse headroom = 147.058823529 fuse amps
That is right on the limit of pure copper 4 awg wire with 90C insulation by ABYC rules.
If it was me I would go to 2 awg to minimize the ripple.
If you are going for NEC rules then 1/0 awg is indicated.
Glad you asked.Thank you for the explanation. Do you have a source or is this just a tribal knowledge thing? Not questioning, just wanna see what other stuff I can learn as well.
Your MCB from SCC to Battery should be at least 20AMP, not 50 AMP. the current that will flow from the SCC to battery is almost the same from Solar Panel to SCC. and then from battery to inverter, it should be at least 90 or 100 amp. if you calculate the max current that will flow from battery to inverter it is only 83.33 max. Since you cant find 90amp you can go to the next available Amperage.Does the sizing on my breakers and fuses look OK? Any suggestions on wire gauge?
Thanks
It's fine to have slightly larger breakers so long as the cable is specced for the amps. And the current can be different between panels and mppt and mppt to battery. Not sure where you got that idea, if voltage goes down current goes up. It's a 40a mppt so 50a breaker is reasonable.Your MCB from SCC to Battery should be at least 20AMP, not 50 AMP. the current that will flow from the SCC to battery is almost the same from Solar Panel to SCC. and then from battery to inverter, it should be at least 90 or 100 amp. if you calculate the max current that will flow from battery to inverter it is only 83.33 max. Since you cant find 90amp you can go to the next available Amperage.