  1. C

    Option Test cmd1, what meaning??

    Hello, I have this option in the Solarman app for my inverter, if I turn it off it lowers the loads on the inverter and the production remains higher, and if I turn it on they go up and are even with the production of the PV. I don't have batteries, and I don't export to the grid either.
  2. C

    Megarevo, how to power Orange Pi

    I have a Megarevo inverter. I want to install an Orange Pi to use with Solar Assistant, I want to know what recommendations you give me to energize the Pu inside the inverter, or in the Wireway. We did the installation, but I forgot how to power it without having to use a power extension cord.
  3. C

    Megarevo 10kw load 1 and load 2

    47.8 x 240 = 11,472 My manual says 41.7a
  4. C

    Megarevo 10kw load 1 and load 2

    Yes, that's how I understand what it should be. But maybe I worded the question wrong, and her answer confused me. So if the connection is made in only load 1, the inverter must support and withstand 10kw?
  5. C

    Megarevo 10kw load 1 and load 2

    That is also my understanding that the inverter is 10kw, and should provide 10kw in a single load output, but according to MR's response it makes me understand that both loads provide 5kw for a total of 10kw. So I want the installer to do the job right so there are no problems since the house is...
  6. C

    Megarevo 10kw load 1 and load 2

    Yes, I think there is also a language barrier in which it is perhaps difficult to communicate. This would be the question I asked MR.
  7. C

    Megarevo 10kw load 1 and load 2

    Exactly, then how should it be connected to use the full capacity of the inverter? Any diagram or instructions for 120/240?
  8. C

    Megarevo 10kw load 1 and load 2

    Exactly, the megarevo staff told me the information found in the message. Meaning that if I want to be able to use 10kw, I have to use the two load outputs.
  9. C

    Megarevo 10kw load 1 and load 2

    Could you tell me or draw a way that can be done? The house is from Puerto Rico.
  10. C

    Megarevo 10kw load 1 and load 2

    The question comes because in order to use the 10KW of the inverter, you have to use the two Load outputs. Load 1 and Load 2. Then the electrician will take both loads to join them as in the drawing to have 120 on one side, and 120 on the other to give a total of 240 and thus energize both...
  11. C

    Megarevo 10kw load 1 and load 2

    I have this inverter, loads 1 and 2 are being joined together to make just one. According to the manufacturer, load 1 is 5KW, and load 2 is the same. Load1 5KW + Load 2 5KW for = 10KW. You have to add both to give 10kw to the house. The red connection found in the red part of the wireway will be...
  12. C

    EG4 8k (Megarevo)

    Ant update with zero export?
  13. C

    EG4 8k (Megarevo)

    Hi, Any update?
  14. C

    Powmr 10k vs Srne 10k?? Hybrid inverter 120/240

    Which brand is better, or which one would you choose?
  15. C

    Where to install? Indoor inverter for semi indoor

    Hello, I would like to know your opinion. I bought a Powmr 10k inverter. It is for indoor use, but I had thought to install it in the place of the black mark in the photo. The rain does not enter the garage, but perhaps the dust or a little dirt like anywhere else.