If you are going direct burial then thhn/thwn won't work because neither is rated for direct burial. Not sure if the windy nation wire you reference is direct burial rated. 10-2 ufb cable is common at most "depot" stores and is DB rated. It will have 3 conductors. If you only need 2 per run ...
Nevada , AZ. In 2017 the Nec was amended to attempt to take some of the speculation about what is considered a structure. A light pole has been given an exemption if the pole is a manufactured part of the lighting system .
Billboards , electric signs, airfield towers etc... anything with an...
I just received an email from signature solar stating they do not provide any support for the generator start feature on growatt inverters despite the fact that the feature is listed in the literature.
Is this an off grid inverter?
Is it a 2 wire start system ?
If so , are your control wires...
Most places allow " owner - builder" permits. You simply must act as a contractor. Draw a set of plans and submit them to the local AHJ. The city or county engineer will approve or deny the plans. Pay the fees , get inspections and you can turn those docs into your homeowners insurance to...
Lightning protection and equipment grounding are two different things.
An airport rotating beacon on a 60ft metal tower has 2 "grounds". The ground from the rotating light fixture on the tower ties into the electrical systems egc as usual. The lightning rod on the tower is bonded to the tower...
There is a guy in town who swears by these carbon foam batteries.
I have a few questions...
Are they any better than lead acid?
Why do the marine guys like these batteries so much?
How well do they perform in the heat? We have 96-100 °f highs and around 86° f lows daily in August.
Can...
Hello,
My home is off grid and yes 120/240 single phase.The home has propane for heating ,cooking and hot water.
My largest load will be a 240v 30k btu ac unit ,manufacturers data sheet says it consumes 3380w, around 11000w at start up.
I estimate a daily usage of 48,000wh for 6 mos of...
Baja Mexico. August . Avg 95-105 °f , 44% humidity
1000 sq ft home .
One each: 1 and 2 ton inverter 19 seer mini splits.
2 occupants.
Home is made of insulated block.
Avg usage 29k daily.
No one is getting shocked by an electrical system because they walked into an area between 2 rods that were properly grounded. Electricity takes the easiest path to ground. If you're not it, you're not getting shocked.
You are more likely to get shocked by a poorly grounded system . A bad...
Either solid or stranded will do as long as it's copper. Stranded will be a lot easier to pull.
If you have more than 3 current carrying conductors in a piece of conduit you have to derate the ampacity of the wire. If the conduit is on the roof there are ambient temperature correction factors...
No wire splices are allowed in the conduit. The splice must be accessible . It must be located in a box.
I would use a insulated multi tap connector instead of a butt splice
So you have shipping in the U.S to your desired location. Vendor charges you this. Most companies are reluctant to ship to Mexico. They will ship it to a U.S. location and then you can hire an international shipper to transport it to Mexico.... you pay again ....in addition to that you then...
That's too much for me to mix. Those days are gone. I would turn to dust and blow away.
On 12" diameter holes I like to make 2x4 wood wedges(1-1/2 - 6" thick ) and use them to pin the pole in the center of the hole. I use 3 per hole and it leaves adequate room to get the mud around. Great time...
I agree it's the interpretation of " structure ".
The nec definition of " structure " is " that which is built other than equipment " . Every inspector I've ever had considers the electrical sign on the pole the equipment and the pole and base the structure.
Check those battery switches, most of them are rated at 48vdc , lithium batteries operate beyond that voltage rating. Blue Sea has stated their switches are not to be used beyond rated voltage.
Hello,
Does anyone know of any reliable solar equipment suppliers in Baja Mexico? Bringing gear from the U.S adds 19% tax to the equation. I found some companies on the net but they only wanted to sell packages that they install.
Thanks
So I went on a job today to help a local guy install 2- Outback Radian Gs8048A inverters. After we finished up and commissioned the system , I noticed a sol ark 9k 240vac inverter on the wall , nothing attached, not in use. It's too small, so they went with the 2 new 8k units. Local guy thinks...
Are you using watchpower app?
After you connect to the wifi module it should prompt you to confirm the connection, then ask for your wifi router and password. Then it should reboot and connect.