I think new "inverter" heat pumps have much lower starting current due to the built-in variable frequency drive.
 
I think new "inverter" heat pumps have much lower starting current due to the built-in variable frequency drive.

Lower?

Yes for LRA, but the DC power supply capacitors don't get powered until the contactor is engaged by the thermostat, that has its own surge charging the DC power rail for the inverter for a few 60 hz cycles.
 
Lower?

Yes for LRA, but the DC power supply capacitors don't get powered until the contactor is engaged by the thermostat, that has its own surge charging the DC power rail for the inverter for a few 60 hz cycles.

Oops, Yes that makes sense.
 
Another thing is that presumably the heat pump has a compressor and they can have a huge inrush current when they start up. That might overload the backup port causing the inverter to shut it off.
Thanks, it shouldn't be a problem, heapump is rated with 5A max i think. It also has gradual startup mode to avoid exactly what you're talking about. But yeah, I may just keep inverter plugged into the grid all the time and use timers.
 
I have question. This is our inverter. How do I set this type of inverter not to export power to the grid? We have a uni-directional type of electric meter. So even if we are exporting our surplus power our bill still increases. IMG20231023145342.jpg
 

Attachments

  • IMG20231023145342.jpg
    IMG20231023145342.jpg
    438.8 KB · Views: 0
How do I set this type of inverter not to export power to the grid?
You will need to enable export power limitation feature and set the export power level to 0W.

Note, however, that will not _totally_ prevent any export - a brief export of power will happen due to the time it takes the inverter to reduced its output when a house load is switched off.
 
Good afternoon

I can't charge my batteries in "self user" on Solis inverter S5(5Kw) with a DIY LifePo4 S16 105Ah Battery with Daly BMS.

The Battery on Solis are configured as "Lead Acid Battery", and charges me from the GRID with the "Self User", even with settings "STOP" and "Not Allow charging from Grid".

I can't understand how to configure this crazy inverter. It seems that any configuration does something different.

I'm already tired of breaking my head.

I'm waiting for my new Seplos 100A BMS to connect via CANBUS to see if I can solve this problem once and for all.

The only way to charge the batteries so far, is setup the inverter in mode "BUCKUP", but then I have to put it in "Self User" overnight to discharge the batteries on the gridit. Doesn't make any sense.

The mode "Self User" does not do the proper functions. 1-Solar, 2-Batteries and 3-Grid

Anyone using a Diy LifePO4 16s 100A battery and this inverter can help me?

Thanks
 

Attachments

  • IMG_20240214_075512.jpg
    IMG_20240214_075512.jpg
    207.1 KB · Views: 6
  • IMG_20240214_075536.jpg
    IMG_20240214_075536.jpg
    194.7 KB · Views: 6
  • IMG_20240213_183527.jpg
    IMG_20240213_183527.jpg
    214.7 KB · Views: 6
Thank's SeaGal

I don't want to charge the baterry from the Grid, only by the sun.

What I read is that we shouldn't activate "run" if we want to charge from solar.

It's right?
 
No, just self-use mode will charge batteries from PV, assuming more PV is being generated than your house usage.
 
Well... I don't think they're doing that in Self User
Now, even with the batteries, after the sun goes down, it turns off.
Damn inverter, I'm fed up with this inverter.
 

Attachments

  • IMG_20240215_164416.jpg
    IMG_20240215_164416.jpg
    152.4 KB · Views: 4
Is the smartmeter connected? What are the meter settings on the inverter? It says your house is using 0W so something's not right
 
Also, it doesn't look like your CANBus connection is set up correctly; it might not be detecting your battery correctly unless you have configured the Solis to recognise your battery comms.
 
Is the smartmeter connected? What are the meter settings on the inverter? It says your house is using 0W so something's not right

Sometimes consumption appears in house, other times it doesn't.

But it is not the consumption, it is limited in the inverter to not injecting into the grid

As I say Damn inverter.........
 

Attachments

  • IMG_20240213_184121.jpg
    IMG_20240213_184121.jpg
    145.5 KB · Views: 2
  • IMG_20240213_184050.jpg
    IMG_20240213_184050.jpg
    142.5 KB · Views: 2
  • IMG_20240213_184034.jpg
    IMG_20240213_184034.jpg
    118.8 KB · Views: 2
  • IMG_20240213_184007.jpg
    IMG_20240213_184007.jpg
    226.8 KB · Views: 2
  • IMG_20240213_183911.jpg
    IMG_20240213_183911.jpg
    160.9 KB · Views: 3
  • IMG_20240213_180624.jpg
    IMG_20240213_180624.jpg
    93.4 KB · Views: 3
Also, it doesn't look like your CANBus connection is set up correctly; it might not be detecting your battery correctly unless you have configured the Solis to recognise your battery comms.

I don't have CANBus connection.

Solis configured as Lead acid, but BMS daly manages battery charges Diy LifePO4 S16 100A.
 

Attachments

  • IMG_20240213_183520.jpg
    IMG_20240213_183520.jpg
    120.8 KB · Views: 1
  • IMG_20240213_183527.jpg
    IMG_20240213_183527.jpg
    214.7 KB · Views: 1
OK so there's a problem with the smartmeter. If it can't measure power use by the house, the inverter can't know what power it should output.

How did you wire the meter? Please make a schematic.
 
Basically and sorry for my drawing that looks like it was made by my son.

The meter is a sdm120ct and it is ok. I can confirm with Shelly EM that I also have installed on the grid

the difference in the meter is the is from (system 2) that is producing what the house is consuming.
 

Attachments

  • ESQUEMA.jpg
    ESQUEMA.jpg
    170.1 KB · Views: 4
The schematic looks correct

On the photo, your SDM120 displays 0.0W which would be unusual for a house

> Sometimes consumption appears in house, other times it doesn't.

What does this mean?

I see you have microinverters. This is similar to my situation: I have a Solis S5 and a Fronius inverter with panels on another roof.

One little detail about Solis that is not mentioned in the manual is this:

- If you set maximum export power in Solis to "X" Watts

- If your microinverter installation (or my Fronius) produces a lot more than "X", the house uses little power, as a result more than "X" watts are exported to the grid even if the Solis produces nothing

- Solis detects this, thinks it's an anomaly, and shuts down. But it doesn't say it is shut down! It just stops working.

Solution is to set "Max export power" to more than what your microinverters can produce.
 
Thank you very much for all the help.

Today I got back from Solís and installed a BMS Seplos V3 and realized that the CT was messing everything up.

If you live in one direction, the CT already charges the battery and if you reverse the direction, it stops charging and consumption remains at 0w.

But just change the phase with the neutral in the CT connection and I'll get crazy values.

Any tips or manual for the correct configuration direction.

Regards
 