UPC Uninteruptiable Power Supply Battery Replacement

I thought floating for LFP isn't recommended...
It isn't.

Lithium batteries (including LFP) suffer the most stress at 100% SOC (SLA is at 0% SOC, they like to be constantly float charged). This is why folks with EVs often terminate charge at 80% or 90% to extend the service life of their batteries.

Lithium also wants very precise termination voltages, SLA is very tolerant of sloppy voltages.

I worry that with the wide variance in SLA charging designs and tolerances, an LFP pack will be abused.

Mike C.
 
Do you have any real world observations to prove that it doesn't hurt the battery?
Only my own personal experience.
I haven't overcharged (above 3.65v per cell) , or over discharged (below 2.5v per cell) . And I don't push them hard (I stay at or below 0.2c rate). Or let them get too hot/cold.
But I do charge to the top of the knee (3.56v percell) , and float there (3.5v per cell) daily.
The only degradation I have seen is calendar aging (1% per year).
I also have one battery that I used to charge to 3.625v per cell, daily.
Which is now part of a portable system that doesn't see much use. And just floats 24/7 at 3.5v per cell.
I have only been running LFP for a little over 2 years. But I see no reason for the results to suddenly deviate from the expected.
Is the same true if floating at lower voltages than 100% SOC ?
Yes
But you will limit capacity if you don't balance the cells regularly, in the upper knee (Above 3.45v per cell).
 
Only my own personal experience.
I haven't overcharged (above 3.65v per cell) , or over discharged (below 2.5v per cell) . And I don't push them hard (I stay at or below 0.2c rate). Or let them get too hot/cold.
But I do charge to the top of the knee (3.56v percell) , and float there (3.5v per cell) daily.
The only degradation I have seen is calendar aging (1% per year).
I also have one battery that I used to charge to 3.625v per cell, daily.
Which is now part of a portable system that doesn't see much use. And just floats 24/7 at 3.5v per cell.
I have only been running LFP for a little over 2 years. But I see no reason for the results to suddenly deviate from the expected.

Yes
But you will limit capacity if you don't balance the cells regularly, in the upper knee (Above 3.45v per cell).
Interesting...
Did you notice any bloating of the cells?
What cells are you using (brand, Ah, etc...) ?
 
I thought floating for LFP isn't recommended...

It depends on what voltage it is floating. I would float a 12v LFP at 13.6 forever and not give it a second thought. And I'm pretty sure Bluettis and similar float too while left plugged in. What good is a power station if it's not ready to go?
 
And I'm pretty sure Bluettis and similar float too while left plugged in. What good is a power station if it's not ready to go?
I'd say they don't really care as long as it outlasts the warranty. On the other tentacle, you _should_ be able to fully charge it and leave it for a year, no?
 
The idea to use LPF as UPS batteries has appealed to me too. Wondered about it.
I am glad to have found this thread.

I guess SLA, AGM and LPF each has its own place.
 
Last edited:
The idea to use LPF as UPS batteries has appealed to me too. Wondered about it.
I am glad to have found this thread.

I guess SLA, AGM and LPF each has its own place.
We use UPS at customer's houses to keep their phone service working in the event of a power outage. Back in the days of copper we only had to fire up a generator at the CO and everyone's dial tone would continue uninterrupted. Now, in the days of fiber, the backup power has to go at the CO as well as at the customer's premisis. Lead acid varieties of UPS do not seem to last more than a few years on average. It would be great to find a good LFP solution.
 
Is there any reason that I could not remove the worn out SLA battery from a small APC battery backup and replace it with a LFP battery? Obviously the UPS was designed for use with a SLA battery, but the BMS in the LFP replacement should keep everything happy...or at least safe, right?
Here we go again. First investigate the specs of the UPS before throwing money at it. Most have a garbage stepped-wave output that your protected electronics will hate. Additionally the H-bridge is designed to overheat just as the standard battery runs out of power. Adding expanded batteries will not extend the runtime. Even if you run at a fraction of the rated power, the internal timer may ignore the battery voltage and shutdown the UPS anyway.

If you are going to spend money, I would instead look into an “all-in-one” unit that already has the solar input. You can grow the system into a proper prepper. Watch this:
 
At a slightly higher cost, you could go the route of building a diy solar generator, good for daily protection of your equipment (computer, tv system), and good for camping or such.

Basically, just need LiFePO4 battery, inverter, battery charger (pulls from your grid) ...

Advantage is more functionality, good diy project, we aren't reverse engineering UPS internals, etc. Just replacing older tech with newer tech.

Hope this helps ...
 
Here we go again. First investigate the specs of the UPS before throwing money at it. Most have a garbage stepped-wave output that your protected electronics will hate. Additionally the H-bridge is designed to overheat just as the standard battery runs out of power. Adding expanded batteries will not extend the runtime. Even if you run at a fraction of the rated power, the internal timer may ignore the battery voltage and shutdown the UPS anyway.
Yep these things are all possible. In the case of my Cyberpower 1500, it's a pure sine wave model. I saw it had a temp sensor on the output transformer and a fan that ran when inverting. Then I tested the bigger battery while keeping a close eye on it. At a mere 10% load it didn't generate much heat. The estimate of time remaining was comically bad for the whole 4 hour runtime but in the end it only cared about going until it hit the low voltage cutoff.
 
Yep these things are all possible. In the case of my Cyberpower 1500, it's a pure sine wave model. I saw it had a temp sensor on the output transformer and a fan that ran when inverting. Then I tested the bigger battery while keeping a close eye on it. At a mere 10% load it didn't generate much heat. The estimate of time remaining was comically bad for the whole 4 hour runtime but in the end it only cared about going until it hit the low voltage cutoff.
Most but not all are bad. Love my APC “XL” models that are pure sine, low-frequency for starting motors, rated for continuous operation and have external battery connectors. Getting difficult to find nowadays. Downside they are heavy, loud and not very efficient at low loading.
 

Attachments

  • ups.jpg
    ups.jpg
    97.8 KB · Views: 8
  • 35AH battery.jpg
    35AH battery.jpg
    88.8 KB · Views: 7
Most but not all are bad. Love my APC “XL” models that are pure sine, low-frequency for starting motors, rated for continuous operation and have external battery connectors. Getting difficult to find nowadays. Downside they are heavy, loud and not very efficient at low loading.

I do love my APC unit - the external battery config units are getting harder to find it seems. I picked up one of those "twin" sets where there's a whole addon battery designed for it a few years ago. Luckily I have another year or two before I need to rotate the batteries out of it.

I have two cyberpower 1500va units in my living room running my synology and PoE/security gear. And (feels good to be able to say it now) whole home is running on UPS backup from two EG4 Indoor units, so I'd need to burn through 28kWh worth of battery before the smaller UPS's even get touched.
 

Attachments

  • 2024-05-20 21.27.38.jpg
    2024-05-20 21.27.38.jpg
    115.5 KB · Views: 5
At a slightly higher cost, you could go the route of building a diy solar generator, good for daily protection of your equipment (computer, tv system), and good for camping or such.

Basically, just need LiFePO4 battery, inverter, battery charger (pulls from your grid) ...

Advantage is more functionality, good diy project, we aren't reverse engineering UPS internals, etc. Just replacing older tech with newer tech.

Hope this helps ...
I do for sure like the idea of what you are talking about here and I absolutely see the value of the added functionality, but honestly I'm more interested in a nice, neat little package that can sit near my TV and PS5 so in the event of a power outage I can safely power down the PS5. The unit I have now does that, but just barely and the battery in it is about done. About once every month or two, for some reason unknown to me, it will just randomly start squealing like it is dying. I have enough time to power down the PS5 and the TV, then unplug the UPS from the wall and do a hard reboot on it and it is good for another month or three.
 
Last edited:
I do for sure like the idea of what you are talking about here and I absolutely see the value of the added functionality, but honestly I'm more interested in a nice, neat little package that can sit near my TV and PS5 so in the event of a power outage I can safely power down the PS5. The unit I have now does that, but just barely and the battery in it is about done.
So buy another one for $60 and you’re done. Honestly a large fraction of the time I change the battery that wasn’t the problem, so I buy the battery and then buy a new UPS. 🤷‍♂️
 
So buy another one for $60 and you’re done. Honestly a large fraction of the time I change the battery that wasn’t the problem, so I buy the battery and then buy a new UPS. 🤷‍♂️
Yeah, for sure, that is an option. I was really hoping to find a good solution using LFP for better longevity so I am not needing to replace this every year or two!
 
I've always wondered why you can't buy proper LFP UPS right now. The lead acid ones are such garbage. But I guess the only thing the market cares about is being cheap to buy and then just throwing away the UPS in a few years when the lead acid battery dies.

I just checked APC and Cyberpower websites... They are selling Lithium battery units. They are all rackmount and pricey. Cheapest one I saw was $479 for a 500VA.
 
I actually find AGM as a good replacement for the SLA battery commonly used in the smaller UPSs.

I have a small UPS running some network gear. I also have two other UPSs for computers.

I find that what kills these small SLA batteries is mainly heat. Even my largest UPS which has two fans, recently died on me, because batteries were bloated and cracked.

Anyways, about two years ago (07/2022) I bought a 25Ah AGM battery to replace the dead 9Ah SLA in my networking UPS.
As this battery is larger and because I wanted to better dissipate the internal heat of the UPS, I extended the battery cables out to the battery.

This works very nicely with the battery being external. The UPS has been through some power outages (2-3 hours each) and performed well (loads are pretty low).

The battery floats at 14v. So far no issues.

I did consider using Lifepo4, but was worried about it being floating for so long.
 