Hey Guys, I have changed the batteries in my system (XW+ 6848, XW+5548, 1x80A Schenider CC, 2x 60A Schneider CC). I had some old Absolyte batteries, just about useless at this point. This is an older system from 2013 that I inherited with the house.
I now have 3x EG4 LifePower4 batteries.
Connected everything, adjusted the battery settings in my InsightHome on the Charge Controllers to the provided EG4 Voltages. Batteries are set as "Custom" in the config for now.
Fired up and ran the system late in the afternoon (sun almost down), everything ran fine. House ran on battery power until just before midnight before voltage dropped enough to switch over to the grid. House continued running.
Next morning when the sun came up the system started charging as it would/should. When the battery voltage was sufficient the inverters started selling.
At some point in the late morning (around 11am) the XW+6848 (the Master) had a failure. The DC Bus Disconnect breaker (that's how it is labeled) for that inverter tripped. I was summoned by my wife because the house had no power. Attempting to reset the breaker resulted in a sizzle and pop and the breaker tripped immediately.
At this point, while I continue to figure out what actually failed on the inverter, I would like to configure the system to run with just the single XW+5548, this should still supply the house.
Do you think this is possible with the failed inverter still connected but powered off?
I am getting an F66 Fault - Multi Unit Configuration settings are incorrect, Make sure only one unit is configured as the Master.
The failed inverter is off.
I have set the XW+5548 to be a Split Phase Stand Alone unit in Multi Unit Configuration, shortly after reboot it throws the same Fault.
Any thoughts?
Thanks
I now have 3x EG4 LifePower4 batteries.
Connected everything, adjusted the battery settings in my InsightHome on the Charge Controllers to the provided EG4 Voltages. Batteries are set as "Custom" in the config for now.
Fired up and ran the system late in the afternoon (sun almost down), everything ran fine. House ran on battery power until just before midnight before voltage dropped enough to switch over to the grid. House continued running.
Next morning when the sun came up the system started charging as it would/should. When the battery voltage was sufficient the inverters started selling.
At some point in the late morning (around 11am) the XW+6848 (the Master) had a failure. The DC Bus Disconnect breaker (that's how it is labeled) for that inverter tripped. I was summoned by my wife because the house had no power. Attempting to reset the breaker resulted in a sizzle and pop and the breaker tripped immediately.
At this point, while I continue to figure out what actually failed on the inverter, I would like to configure the system to run with just the single XW+5548, this should still supply the house.
Do you think this is possible with the failed inverter still connected but powered off?
I am getting an F66 Fault - Multi Unit Configuration settings are incorrect, Make sure only one unit is configured as the Master.
The failed inverter is off.
I have set the XW+5548 to be a Split Phase Stand Alone unit in Multi Unit Configuration, shortly after reboot it throws the same Fault.
Any thoughts?