Hi all,
I have a Schneider XW Pro with a generator wired in per the manual for "Off-Grid".
The inverter recognizes the generator power, qualifies it, tries to charge, but then draws 20amps @ 240VAC from the generator no matter what parameters I choose.
I tried adjusting the generator breaker size, Max bulk charging current, Max percentage charge rate based on battery capacity, etc.
None of these parameters seem to help. Changing the generator breaker size should be all I need to do to change the charge rate from the generator, as shown in David Poz's video on this.
HOWEVER!! I am using firmware 2.04. I tried loading 1.11 BN0049 and it works perfectly! It adjusts the charge rate based on the generator breaker size without changing ANY other parameters.
Has anyone else noticed this issue? Is there something I'm missing that is causing the issue aside from the firmware? Could having AC coupling turned off under "Inverter" in the settings cause an issue with phase alignment? I considered reloading 2.04 but at this point I want to just leave it alone to avoid further issues. If it ain't broke....
I have a Schneider XW Pro with a generator wired in per the manual for "Off-Grid".
The inverter recognizes the generator power, qualifies it, tries to charge, but then draws 20amps @ 240VAC from the generator no matter what parameters I choose.
I tried adjusting the generator breaker size, Max bulk charging current, Max percentage charge rate based on battery capacity, etc.
None of these parameters seem to help. Changing the generator breaker size should be all I need to do to change the charge rate from the generator, as shown in David Poz's video on this.
HOWEVER!! I am using firmware 2.04. I tried loading 1.11 BN0049 and it works perfectly! It adjusts the charge rate based on the generator breaker size without changing ANY other parameters.
Has anyone else noticed this issue? Is there something I'm missing that is causing the issue aside from the firmware? Could having AC coupling turned off under "Inverter" in the settings cause an issue with phase alignment? I considered reloading 2.04 but at this point I want to just leave it alone to avoid further issues. If it ain't broke....