Beware of the APEXIUM BOX Connectors

Looks like a quick release systeem that burns out
Only reason is that it not have a good connection on it.
And it heat up till it meld and more lose it come and more heat come .
I do not like systeem that you can easy connect or disconnect.
By use it worn out and you have a bad connection.

Wel if this is the problem never use a systeem like that again
And its good that you have find it and worn others about it.

Good luck
 
Beware of the APEXIUM BOX this happened with the connectors they proved with the box.
Looks like it is designed for two cables in parallel, only one burned up.
Were you using two? If so, it possible the undamaged one has slightly higher resistance, so the other one took the hit.

How much current was going through there? 50mm^2 welding cable is rated for 255-345A depending on manufacturer.
Not clear what the connector is rated for, but I would guess 200A.
 
Looks like it is designed for two cables in parallel, only one burned up.
Were you using two? If so, it possible the undamaged one has slightly higher resistance, so the other one took the hit.

How much current was going through there? 50mm^2 welding cable is rated for 255-345A depending on manufacturer.
Not clear what the connector is rated for, but I would guess 200A.
The connector is rated for 200A, It is a 50mm2 wire and the inverter was set to charge and discharge at a max 160A.
 
Last edited:
The table above assumes a cable length of approximately one meter. If you want to use longer cables, the guideline is to increase the cable diameter from 2 meters. E.g. 12 volts, 1500 watts, becomes 35mm2 instead of 25mm2 cable.

Picture is in Dutch so translation will come .
2e picture is the translation of it .

I hope some help with this.
 

Attachments

  • IMG_20240618_151329681.jpg
    IMG_20240618_151329681.jpg
    167.1 KB · Views: 11
  • Screenshot_20240618-152121.png
    Screenshot_20240618-152121.png
    463.4 KB · Views: 10
Last edited:
Hmmm... my schoolgirl maths tells me that a diameter of 50mm would be an area of 25*25*3.14 = 1962mm^2 - that's big!
Sounds too big. I really wish the vendors would publish the part numbers for these connectors.
Maybe they couldn’t fit the 2 superscript for mm^2

I read the Apexium specs and manual and found nothing.
So I don’t know why the connector says 50mm.
 
Looks like it is designed for two cables in parallel, only one burned up.
Were you using two? If so, it possible the undamaged one has slightly higher resistance, so the other one took the hit.

How much current was going through there? 50mm^2 welding cable is rated for 255-345A depending on manufacturer.
Not clear what the connector is rated for, but I would guess 200A.
I think the second connector is for daisy chaining a string of them in parallel.
 
Sounds too big. I really wish the vendors would publish the part numbers for these connectors.
Maybe they couldn’t fit the 2 superscript for mm^2

I read the Apexium specs and manual and found nothing.
So I don’t know why the connector says 50mm.
Ist not 50mm but 50mm2 .
So i mis the 2 on the end.
I have see that a lot in the automotive world .
That is my old job and dont ask me wy ?
Think that those people think you know that it never can be 50mm .
 
Last edited:
Wow, sorry that happened.
Do you have any more photos of the back side with everything still connected?
1000010149.jpg

Is that a washer?
1000010152.jpg
 
When I inquired about the apexium box and asked if cables were included she mentioned that the connectors were included to make your own cable.
Screenshot_20240618_092654_Samsung Notes.jpg
 
Unless I am mistaking what the images are showing it looks like this right angle connector is designed for push on quick connect. If so that is a design connection fault area. Since the damage seems greatest at this connection zone, even thought there is also some damage at the bus bar bolt area, I would agree that this type and brand of connector should be avoided.
 
Unless I am mistaking what the images are showing it looks like this right angle connector is designed for push on quick connect. If so that is a design connection fault area. Since the damage seems greatest at this connection zone, even thought there is also some damage at the bus bar bolt area, I would agree that this type and brand of connector should be avoided.
not really...
at least the seplos ones are rated for 500A , but you do need to push until they click.
so either this one had a production error, or it wasn't fully pushed in
 
Unless I am mistaking what the images are showing it looks like this right angle connector is designed for push on quick connect. If so that is a design connection fault area. Since the damage seems greatest at this connection zone, even thought there is also some damage at the bus bar bolt area, I would agree that this type and brand of connector should be avoided.

The other option would be not completly pushed on. Or with the OP stacking batteries and doing a Z wire configuration (in accordance with the manual/common practice) verse using bus bars the connection just plain overheated. Thermal image of wires in this configuration are pretty stark - the first and last connection from the box to the inverter is taking current from the whole stack

To the OP - you have a stack of batteries - was this connection on the top/bottom or somewhere in the middle?

And it could just be a bad connector on the wire.

Hopefully they send him a new wire and box connection to fix the issue.

and IMO were I to do a stack of batteries I would use bus bars for all the connections to keep the current even and I would connect my uplinks between the 1&2 and 3&4 battery to keep the balance dead even. This is per the thread about paralleling batteries and the answers are not intuative but the math is.
 
Unless I am mistaking what the images are showing it looks like this right angle connector is designed for push on quick connect. If so that is a design connection fault area. Since the damage seems greatest at this connection zone, even thought there is also some damage at the bus bar bolt area, I would agree that this type and brand of connector should be avoided.
These no-name connectors are basically knock-offs of the Amphenol Industrial SurLok Plus series of connectors.
It's difficult to trust the knockoffs, because I have yet to see a data sheet with full specifications.
Yes, I realize there is no choice when you buy the gear.

For reference, I use the Amphenol ones for my DIY stuff because I know the company stands behind them.
No, I don't know if they are interchangeable with knockoffs, probably not.
 
These no-name connectors are basically knock-offs of the Amphenol Industrial SurLok Plus series of connectors.
It's difficult to trust the knockoffs, because I have yet to see a data sheet with full specifications.
Yes, I realize there is no choice when you buy the gear.

For reference, I use the Amphenol ones for my DIY stuff because I know the company stands behind them.
except.. they are not no-name ( in the seplos boxes), they are futronics , and are use in all BYD busses and cars, and they are certainly no knock-offs
 