- Change your ANL fuses to a different type.
- To the inverter use a class T.
- On the battery post use a MRBF.
- You don't need to fuse the MPPT line to the bus bar.
- With 1 string of panels you don't need a fuse at all. If you choose to fuse it use a MC4 fuse.
You may want to switch to 48v to avoid 333amps and the larger wire and fuses.
If you already have parts you can't exchange I understand sticking with 24v. All wires 20% over max expected current. All wire the same. The mrbf should be 20% over max BMS output.