6000xp Question

Hernandezdave

New Member
Joined
Jul 12, 2024
Messages
7
Location
Texas
Good morning everyone!

I have a 6000 Xp installed currently with no solar as I am waiting for some additional panels and wiring.
I have ac in from the grid into inverter. Ac out feeding a sub panel.
I have a 850 AH 480v batttery connected on the battery Input side.

Question is that when I am powering devices and both grid and ac out are on it pulls all the power from the grid. When I turn off the grid breaker it pulls everything from my battery.

Am I missing a setting so that it powers from my battery first and then switches to the grid only when the battery can no longer handle it? It seems like it is prioritizing the grid only.
 
What is your #14 "AC charge setting set to? I have mine set to 20% and end at 40%. My system never uses grid. Also make sure you're in EPS mode.
 
Am I missing a setting so that it powers from my battery first and then switches to the grid only when the battery can no longer handle it? It seems like it is prioritizing the grid only.
Look into AC First timings and make sure the setting under the Discharge section are appropriate.
Which basically means Battery SOC/Voltage is not in Grid Fallback range.
 
Thank you everyone for your help! System is back up and functioning as it should.
Also, thank you so much DiyRich for your help.
 