OK, so I made a mistake and bought some equipment before I had any understanding of what the heck I was getting into. I don't want to send anything back as I think we will eventually grow into this system by next summer. Right now we are living in an RV in Colorado while we build, and will be in the RV over winter. I want to get enough solar and storage going to make sure we can run the propane heater in the RV every night.
This is a place to put down notes as I learn and hopefully get some feedback if I am making egregious errors.
I have purchased the following:
(1) LV5048 5kW 48V Inverter
(4) 24V A123 LFP Battery Box w/ BMS
The manual for the inverter suggests at least 200aH of battery storage, and the battery bank needs to be 48V. My batteries are rated at 24V 92.8aH. So I need to connect (2) 24V batteries in series to get to 48V. Doing this with my 4 batteries now gives me (2) 48V 92.8aH packs. Putting these in parallel would give me 48V at 185.6aH. This falls below the recommended 200aH for the inverter. What are the drawbacks of only using 185.6aH? Need to research more about that. The solution would be to buy (2) more of the batteries, wire them in series and then add them in parallel, which would give me 278.4aH at 48V. But that means another $1800.
For panels, I am looking at the following panels:
Used 250W 24V 60 Cell Poly Solar Panels
The manual for the inverter states that the maximum PV array open circuit voltage is 145Vdc. This means I need panels that will stay under 145Vdc open circuit voltage? The listed open circuit voltage for the panels I am looking at is listed at 37.6V. This is obviously well under the inverter maximum. However, for solar panels to be able to charge batteries, the voltage of the panels needs to be higher than the voltage of the batteries. Since my batteries are 48V, the voltage of my solar panels needs to be higher.
Single panels in parallel will not give me high enough voltage. For the panels I am looking at to work, I would need to wire two in series. That would give me250W 75.2VOC on the panels. I think this VOC is high enough to charge the batteries but low enough to not damage the inverter.
In the video I watched about the LV5048, it was mentioned that only 400W at a time can be added in solar panels. Since the panels I am looking at are 250W, I am not sure how to proceed. I need to learn more about this.
This is a place to put down notes as I learn and hopefully get some feedback if I am making egregious errors.
I have purchased the following:
(1) LV5048 5kW 48V Inverter
(4) 24V A123 LFP Battery Box w/ BMS
The manual for the inverter suggests at least 200aH of battery storage, and the battery bank needs to be 48V. My batteries are rated at 24V 92.8aH. So I need to connect (2) 24V batteries in series to get to 48V. Doing this with my 4 batteries now gives me (2) 48V 92.8aH packs. Putting these in parallel would give me 48V at 185.6aH. This falls below the recommended 200aH for the inverter. What are the drawbacks of only using 185.6aH? Need to research more about that. The solution would be to buy (2) more of the batteries, wire them in series and then add them in parallel, which would give me 278.4aH at 48V. But that means another $1800.
For panels, I am looking at the following panels:
Used 250W 24V 60 Cell Poly Solar Panels
The manual for the inverter states that the maximum PV array open circuit voltage is 145Vdc. This means I need panels that will stay under 145Vdc open circuit voltage? The listed open circuit voltage for the panels I am looking at is listed at 37.6V. This is obviously well under the inverter maximum. However, for solar panels to be able to charge batteries, the voltage of the panels needs to be higher than the voltage of the batteries. Since my batteries are 48V, the voltage of my solar panels needs to be higher.
Single panels in parallel will not give me high enough voltage. For the panels I am looking at to work, I would need to wire two in series. That would give me250W 75.2VOC on the panels. I think this VOC is high enough to charge the batteries but low enough to not damage the inverter.
In the video I watched about the LV5048, it was mentioned that only 400W at a time can be added in solar panels. Since the panels I am looking at are 250W, I am not sure how to proceed. I need to learn more about this.