Santa
.
- Joined
- Nov 10, 2019
- Messages
- 612
Don't know yet...But can you estimate 10 feet maybe? Subject to change when installing...And how long will that wire be from suitcase panel to the SCC?
Don't know yet...But can you estimate 10 feet maybe? Subject to change when installing...And how long will that wire be from suitcase panel to the SCC?
If your longest run is less than 20 feet then ~23 amps would require 12awg. Up to 30 feet 10awg. So you're good!Don't know yet...But can you estimate 10 feet maybe? Subject to change when installing...
I got 28 amps...? but 10AWG is good. It won't be more than 15 feet I would assume.If your longest run is less than 20 feet then ~23 amps would require 12awg. Up to 30 feet 10awg. So you're good!
Longer than 30 feet you need 8awg.
oops, i see your suitcase is 2 panels. I got your total amps at 29.28.If your longest run is less than 20 feet then ~23 amps would require 12awg. Up to 30 feet 10awg. So you're good!
Longer than 30 feet you need 8awg.
Are you counting the Imp or the Isc?oops, i see your suitcase is 2 panels. I got your total amps at 29.28.
Up to 30 feet you need 10awg. (still good)
Up to 50 feet you need 8awg. (same)
Just saw your post above, yep, you're right. You don't need me anymore!
Attached is the guide i use - i think one of these should be a sticky on this site somewhere.
Holy crap, i learned something very valuable today.Very important to note (since I don't see it noted on that chart anywhere) that those length measurements must be for round-trip circuit length, not one-way. So if the panels are literally 30' away, round-trip distance is 60', and the wire must be sized accordingly.
Thank you! I too learned something new. It won't be over 30 feet roundtrip.Very important to note (since I don't see it noted on that chart anywhere) that those length measurements must be for round-trip circuit length, not one-way. So if the panels are literally 30' away, round-trip distance is 60', and the wire must be sized accordingly.
It's amazing how many wire gauge calculators don't tell you that, particularly given how bloody critical of a consideration it is...Holy crap, i learned something very valuable today.
I'm not a fan of my chart anymore. Do you have one you recommend, one for dummies like me?Very important to note (since I don't see it noted on that chart anywhere)
Here in California, we like to (need to?) park in the shade so having your carry out panels 25+ feet from your RV is not uncommon. Just consider your real world use case.It won't be over 30 feet roundtrip.
I will be mounting 4 on the roof. The suitcase will only come out sometimes. So, for argument's sake, I will be connecting them with the mc4 Y 1-4 combiner and then connect the suitcase with a MC4 1-2 combiner. If I use 10AWG to connect the 4 panels, and let's say I have to move my suitcase panel 25 feet (50 feet roundtrip). Would I need to get 8AWG wire for the suitcase panel to the combiner?I'm not a fan of my chart anymore. Do you have one you recommend, one for dummies like me?
Here in California, we like to (need to?) park in the shade so having your panels 25+ feet from your RV is not uncommon. Just consider your real world use case.
I mean, the chart is still good (albeit a little optimistic in my view), you just have to remember that "circuit length"=ALL wire used in the system. Alternatively, we have a decent calculator and some relevant charts on our site, but you still have to remember to input round-trip length (although at least ours mentions that). I've found, in practice, that our calculator tends to spec heavier-gauge wire than Blue Sea's, which I personally like because I'm a big believer in overkill when it comes to wiring, but I suppose that could be argued.I'm not a fan of my chart anymore. Do you have one you recommend, one for dummies like me?
I'm feeling really unqualified to answer this now...I will be mounting 4 on the roof. The suitcase will only come out sometimes. So, for argument's sake, I will be connecting them with the mc4 Y 1-4 combiner and then connect the suitcase with a MC4 1-2 combiner. If I use 10AWG to connect the 4 panels, and let's say I have to move my suitcase panel 25 feet (50 feet roundtrip). Would I need to get 8AWG wire for the suitcase panel to the combiner?
In my OP, I explained the reason for only sometimes using suitcase. I want as much power as possible, when stealthly possible. Disconnecting the roof panels defeats why I would even mount them in the first place.I'm feeling really unqualified to answer this now...
I "think" that with the addition of 50 foot round trip you would require ALL of the wires to be 8awg. (Justin?)
Alternatively, if you disconnected the roof panels when you add the suitcase, you would be 6.48 amps and good to 100' roundtrip.
What is the use case for the suitcase? To augment the rooftop panels or for use when rooftop not in use? (parked in shade for example).
For the latter, i think you'd be disconnecting the rooftop panels to be safe (trees do fall and shadows move...)
Does that apply to ALL the wiring in parallel? So even the rooftop solar panel leads become woefully inadequate?Ahhhhhh worse than all that... 30A at 50' needs 2AWG
Waaaaaiiiiiiit I'm an idiot... hang on, what voltages are we talking about here? I was thinking 12v, but obviously at the panel side of the controller the voltage is way higher, and the amperage way lower, which of course means you can use lighter-gauge cables.Does that apply to ALL the wiring in parallel? So even the rooftop solar panel leads become woefully inadequate?
You seem pretty smart to me. ;-) 18 on the (4) 100 watt panels and 18.2 on the suitcaseAhhhhhh worse than all that... 30A at 50' needs 2AWG to keep the voltage drop under 3%, though 4AWG puts you at 3.2%, which... eh... could be lived with I guess.
8AWG at that distance puts your voltage drop at 8.08%, which is simply untenable. Then again, running 2ga wires 25' out is also pretty untenable... I strongly recommend just not putting your suitcase that far away, @Santa .
EDIT: I'm an idiot... what voltage are your panels running at? I was using 12v as the voltage in my calculator and on the panel side of the controller, that's obviously not the case.
Yes. There is a limit of 30 amps on this SCC. I HAVE to wire them in parallel with this system. Adding the 5th panel is not what Will recommended in his blueprint and will be close to the max the SCC can handle, and not feasible if the weather is cold, according to what I am understanding, the voltage will rise.Yea, and after I just read back, I am wondering why we didn't suggest connecting the 4 roof panels in series?
Is there a limitation on the SCC for input volts?
(panels in series add the volts, and as we discussed, panels in parallel add the amps).
...okay, so for the purposes of calculation, I'm figuring a max of 9A per panel (and the suitcase has 2?) so I figure 18A @ 18.2v @50' and come up with 8AWG being perfectly fine, but don't go lighter than that... sooooo basically, right back where we started18 on the (4) 100 watt panels and 18.2 on the suitcase
FYI, Combining panels in parrallel that way can be dangerous when the panel count goes over 3 or so. The reason is if any panel develops a problem, it can be back-fed the combined current from all the other parrallel panels, which can have more total current than the wire and panel can handle, posing a fire risk. That's why combiner boxes always individually fuse or circuit breaker each string.
Wouldn't the panels' blocking diodes protect against this?
As long as they're working properly, but I don't like betting on electronic devices proper operation for fire prevention, a fuse or circuit breaker is much safer. If you've ever had a personal encounter with a fire, you'd take every precaution as well.
RE; Suitcase panel: I would LOVE to directly answer your question of "does it (suitcase panel) have an SCC built-in, or is it just the panels" but cannot. Originally, about 2012, I bought an "all-in-one" along with the suitcase panel. The battery/all-in-one was since stolen. I still have the suitcase. This was my introduction into solar/backup power. I don't know or understand what they used as a charge controller. I tried to ask them (Lion) about it, but never got an answer. Is there something on the back of the panel that can answer this?Okay, I've read back... the panels on the roof are roughly 18.2v, 5.5A, so in parallel they're fine all the way to 12AWG.
The suitcase is a little funky... does it have an SCC built-in, or is it just the panels? If it has an SCC built-in, then it's stepping down the voltage/up the amperage, in which case you're back to using 2AWG at 50'. If it's just the panels out 25' away, then you're still high-voltage low-amperage, in which case you're good to stay at anything heavier than 12AWG going to the SCC, then of course heavier gauge from the SCC to the battery.