Hey there!

A little confused with everything I'm looking at, and my setup isn't exactly what I would consider standard, so I would appreciate any resources or advice here.

Looking for feedback on how we may eventually go with a hybrid system with a battery. I am also considering using an EV (such as the Ford Lightning or another EV that allows using as a backup) to backup the house in the event of outages. Either way, it would be great to know how we might eventually get there.

I am getting solar in two weeks with a grid tied system with Enphase microinverters. I know we will not get power when the grid is off in this setup.

I attached a digram of the wiring from the home. Besides the 100A fuse potentially not being enough for the house in the future (especially if charging an EV), wouldn't any sort of inverter need to go between the electrical panels in the house and the grid? I'm not super familiar with how automatic shutoff and transfer switches work, or how you would isolate from the grid.

Image 1 is the current setup of the house.
Screen Shot 2021-07-17 at 1.28.04 PM.png
Both of the electrical panels (house and garage) are connected to the two terminals coming off of the pullout fuse like shown in the diagram there. I imagine that would complicate things when trying to get the load to the house if we were to install a hybrid inverter at some point.



Image 2 is the anticipated setup with solar.
Screen Shot 2021-07-17 at 1.53.08 PM.png


Image 3 is what I imagine we would need to do in the event of getting a hybrid/battery system?
Screen Shot 2021-07-17 at 1.58.57 PM.png

Any feedback or advice would be appreciated! Also I'm not installing all of this myself, this is more just for my own understanding.
 
Welcome to the forums!

A 100 amp fuse in front of a 200 amp load center just means you only have 100 amps available. Assuming the correct wire gauges are in place to support 200 amps, I'd replace the existing pull-out fuse with a 200 amp disconnect.

Other than the junction box, your diagram is similar to how my house is wired, although that puts the onus on you to control power from the load centers if the inverter isn't big enough to handle everything.

More common is to use "critical circuits", that is the inverter isn't large enough to power everything so you just put onto a sub-panel the inverter feeds the things you can't live without.

solar_generator_backup.jpg


Hope that helps!
 
It appears your pull out fuse block has 2 conductors under each lug, which generally isn't legal. (It is hard to tell what terminals might be hidden)

In general it is a bad idea. Run one set of conductors to one of the panels, and make the other a sub-panel. Normally, that means 4 conductors now for the sub-panel.

YMMV.

Good luck.
 