After being up at the cabin for nearly 2 months this winter we discovered a few things. By using the SCP we CAN turn off charging to the lithium modules and pass through power to the cabin load center. The inverter/charger MUST be connected to the batteries to do this though.
This from the solar engineer at NAZWS: "Looks like disabling AC Charge on the SCP would prevent the unit from charging the batteries. To be safe, you may also want to go into the SW 4048 on the SCP and manually set the charger to disabled. There is another setting for the inverter under Advanced Settings->Charger Settings->Auto Chg Enable. This is set by default to disabled, so you’ll want to verify this. If Auto Chg Enable is set to enabled, this will override the charger mode you set previously. So as long as this is set to disabled, and you set the charger to disabled you should be fine. I believe the AC charge would still work, but that is a global command which would perform that setting change on all inverters at once in case you have multiple units in the system. As long as Auto Chg is disabled, you can disable the charger either thru AC charge or disable charger." Good information for others with a similar setup/inverter/charger.
He also said an inverter bypass switch would of course work. However, since my generator outputs only 120vac I guess I'm not clear how I would wire that to the load center to feed both sides of the panel. My inverter/charger outputs 240vac so two hots, neutral and ground. I don't want to continually put on a jumper wire and remove it to go from direct generator feed to the load center to inverter feed. Can I just take 2 hots off the 120vac bypass breaker and feed into both sides of the panel?
This from the solar engineer at NAZWS: "Looks like disabling AC Charge on the SCP would prevent the unit from charging the batteries. To be safe, you may also want to go into the SW 4048 on the SCP and manually set the charger to disabled. There is another setting for the inverter under Advanced Settings->Charger Settings->Auto Chg Enable. This is set by default to disabled, so you’ll want to verify this. If Auto Chg Enable is set to enabled, this will override the charger mode you set previously. So as long as this is set to disabled, and you set the charger to disabled you should be fine. I believe the AC charge would still work, but that is a global command which would perform that setting change on all inverters at once in case you have multiple units in the system. As long as Auto Chg is disabled, you can disable the charger either thru AC charge or disable charger." Good information for others with a similar setup/inverter/charger.
He also said an inverter bypass switch would of course work. However, since my generator outputs only 120vac I guess I'm not clear how I would wire that to the load center to feed both sides of the panel. My inverter/charger outputs 240vac so two hots, neutral and ground. I don't want to continually put on a jumper wire and remove it to go from direct generator feed to the load center to inverter feed. Can I just take 2 hots off the 120vac bypass breaker and feed into both sides of the panel?