Our current codes rate wire current carrying capacity by.. wait for it.... insulation type. However still not saying #6 should be used to carry 300aHas nothing to do with how much current the conductor should carry.
Our current codes rate wire current carrying capacity by.. wait for it.... insulation type. However still not saying #6 should be used to carry 300aHas nothing to do with how much current the conductor should carry.
Not exclusively.Our current codes rate wire current carrying capacity by.. wait for it.... insulation type. However still not saying #6 should be used to carry 300a
Our current codes rate wire current carrying capacity by.. wait for it.... insulation type. However still not saying #6 should be used to carry 300a
Location of the wire plays a larger role in the current carrying ability of the wire…Not exclusively.
Ratings are based on several factors.
Insulation type, plays a bigger role in voltage and location Ratings than amperage Ratings.
I have a video where I push well over 300 amps through 14awg Romex, it passed the current just fine until the insulation lit on fire.If you can watch this YouTube video , a simple 10 AWG silicone wire can handle 100 amps!! I would loose 10 watts for every 100a at 1 ft of distance
Per foot...Whatever you end up doing keep a close eye on it. but I agree with others that you shouldn't.
I'm not an EE but I would say anything over 5% VD is going to wreak havoc with your settings. IE: 10% for sure will. IE: You're charging at 300 Amps, one end of the wire is 14v and but other end will be 12.6.V
Voltage Drop x Amps = Watts = Heat
1.4V x 300A = 420 watts of heat your wire has to safely get rid of.
Its why i pushed to have the subforum added. Its important to see how bad the failures actually are.I can see this thread getting moved to the "Up in smoke" subforum, eventually. Some people have to learn the hard way.
In all fairness the OP is replacing #8 with #6Now I’m going to apply the use on my batteries banks and next maybe my solar panels arrays ( maybe it’s 8 awg all ready) I just purchased 6 awg silicone cables (rated 300a !!!)
Right. I think we were posting at the same time so I wasn't responding to you or really anyone for that matter.Per foot...
umm no 6 AWG is NOT rated for 300Amps power transmission. It could handle it For a microsecond maybe at a foot long.Actually it’s packed with over 3000s fine strands of pure copper wires for high current with of course the silicone rubber insulation for high temperature.. the cable I’ve purchased are from progressiveRC and the 6 AWG silicone wire is rated 300a
Notice the reason this youtuber went to silicone is not to handle heat better, it is to increase the flexibility of the wire.This is how similar I’ll do the build
And this guy still doesn't get it. The number of strands of wire means NOTHING.Here is a review of a 8 awg silicone wire at over 100a under a long duration of time..
What is it you are not understanding?Here is a review of a 8 awg silicone wire at over 100a under a long duration of time..