O Oldsawman New Member Joined Mar 24, 2022 Messages 47 Apr 14, 2022 #1 This look about rite? Appreciate any relative comments
acdoctor Solar Enthusiast Joined Oct 5, 2020 Messages 891 Location Central Arkansas Apr 14, 2022 #2 Looks good to me. 15000 watts from 1 eg4 is very optimistic, maybe that’s a whole rack of them.
Z Zil Solar Addict Joined May 27, 2020 Messages 1,833 Apr 15, 2022 #3 I don't quite see what you are doing with that switch.
O Oldsawman New Member Joined Mar 24, 2022 Messages 47 Apr 15, 2022 #4 acdoctor said: Looks good to me. 15000 watts from 1 eg4 is very optimistic, maybe that’s a whole rack of them. Click to expand... The last system I had I grounded the negative terminal of the lead acid battery bank since the eg4 s are electronic would the same procedure apply? 5 eg4 s
acdoctor said: Looks good to me. 15000 watts from 1 eg4 is very optimistic, maybe that’s a whole rack of them. Click to expand... The last system I had I grounded the negative terminal of the lead acid battery bank since the eg4 s are electronic would the same procedure apply? 5 eg4 s
T timselectric If I can do it, you can do it. Joined Feb 5, 2022 Messages 19,309 Apr 15, 2022 #5 No Most of the inverters, currently available. Tell you not to ground the DC systems. But, check the manual to confirm.
No Most of the inverters, currently available. Tell you not to ground the DC systems. But, check the manual to confirm.