Well what I did was based on what I had read, and kind of based my own judgement on what I thought was right. Thats probably not the best way to go about something but talking with a few different people, we all came to the same consensus. It was a ground rod near the array, bare copper from IronRidge ground mount rack down to the ground rod. The combiner boxes (the metal box itself) are grounded to same frame and ground rod near the array. Since I have a transformerless inverter (a Sol-Ark), I was to NOT ground the PV wires so my combiner boxes have fuse holders for both black and red. The black runs thru fuses, the red. The black is NOT grounded to the ground bus nor metal combiner box. If you have a transformer type inverter, then I don't know, I can't answer the question what you need in regards to ground or neutral, and/or bonding.
I did NOT run any ground wire in my trench. The black and red PV wires are in 2" conduit in the trench to the house and are the only 2 wires in my trenched conduit.
Out at the array, none of that is bonded, because there's no neutral to bond with. There's just the ground rod at the array and the metal rack is attached to the ground rod.
In the house, the Sol-Ark and my critical loads panel Neutral are both tied/connected to my main panels Neutral. The main panel is bonded (ground and neutral connected together) there at the main where the meter base is on the outside of home. The ground there goes down to a ground rod near the home (about 3 feet from the meter base). My home system including my solar system is bonded once and only ONCE. The ground in the Sol-Ark and critical panel are connected to ground in my main panel and from there it goes outside the home to meter base and is bonded there (the same single bond as I described above).
- I figure I have equipment ground, which is the array ground mount frame grounded there at the array for lightning protection.
- I figure the Sol-Ark and critical needs panel relies on Neutral that is bonded there at the meter base.
- I have a system ground which is the ground in my Sol-Ark that makes its way to the critical loads panel and main panel and is bonded with neutral outside my home at the meter base.
I understand the bonding better since I started out with my Sol-Ark not connected to grid nor critical panel. I just hooked up 6 solar panels to it, a 48v battery bank, and a regular duplex receptacle on the wall that I temporarily installed using 3 feet of Romex. I did not have any bonding, and I couldn't get SolArk to run without throwing an error. I then figured out it was the bonding, so I ran a piece of short wire (like 8" long) from grid to ground I think it was there inside the Sol-Ark and viola I had SolArk running without throwing the error. That's when I realized the SolArk HAS to have a way for the power to get back to ground on the Neutral so it has to be bonded to ground, but you only do that ONCE in the entire system meaning your homes electrical system as well. Remove the Neutral wire and you'll see why it needs the Neutral. You cant switch or break the Neutral, it needs to bypass the disconnect/bypass switch as well. Only the L1 and L2 get switched, the N just passes by the switch/disconnect and makes it way over to main panel.
Then a few days ago, I installed the 600 model of the Midnite Solar Surge Protection Device. I asked Midnite if it would work with my combiner boxes the way I had them wired for a transformerless inverter (Sol-Ark) and they said yes. I put one SPD on each combiner box. The SPD does have a ground wire but it is only used if/when theres a lightning strike/surge and that does not disrupt/damage the Sol-Ark I was told by Midnite Solar. I dont know if the SPD's were needed but they make me feel better when theres an electrical storm happening.