Sol-Ark 15K All in One Inverter Released.

Did you watch the two webinars given by Tom Brennan (at the Alt-E conference) that I referenced? (This is an honest question, and is NOT meant to be snarky or disrespectful in any way.)

I did, a couple of times. It is all clear as mud to me. I guess it could be a more generic questions about inverters coupled with micro inverter, not specifically Sol-Arks.
 
I did, a couple of times. It is all clear as mud to me. I guess it could be a more generic questions about inverters coupled with micro inverter, not specifically Sol-Arks.
OK. Just wanted to get your impressions. That is exactly why I 1) accepted the offer of the contact I referenced to use his contact(s) in Sol-Ark to address my concerns/confusions, and 2) posted the same concerns/confusions to this thread. While I wish confusion on no one, it is somewhat reassuring that I am not alone.

Well, the spec sheet for the 15K has both a heading of "Solar Input Power" and "Max Allowed PV Power" of "17000W". For the 12K, the spec sheet has a heading of "Solar Input Power 12000W" and "Max Allowed PV Power" of "6500W + 6500W = 13000W". I believe all those are for DC coupled panel input. Now, given the numbers given for the Sol-Ark 12K in the attachment "Sol-Ark 301 screenshot.png" in post #245, your guess for the amount of AC coupled (via micros or another string inverter) PV panel input to the gen, load, or grid connections is as good as mine (same for the combined input of DC & AC coupled), but the referenced webinars by Tom Brennan seem to state that the AC coupled input limit is at least 20 kW.

Some further research on the subject lead me to this article on the more generic issue by the CTO of Humless.
 
webinars by Tom Brennan seem to state that the AC coupled input limit is at least 20 kW.
I got a feeling that this is correct. The fact that Sol-Ark is now pushing it's own MicroInverters leads me to believe that they intend them to compliment the 15K in having a much higher capacity. I do not think they are doing it to compete directly with Enphase. I suspect they will have some sort of more in-depth communication with the Inverter that goes past just frequency shifting. I am interested to hear the info you get.
 
I got a feeling that this is correct. The fact that Sol-Ark is now pushing it's own MicroInverters leads me to believe that they intend them to compliment the 15K in having a much higher capacity. I do not think they are doing it to compete directly with Enphase. I suspect they will have some sort of more in-depth communication with the Inverter that goes past just frequency shifting. I am interested to hear the info you get.

Yeah, I suspected that the pure number (20 kW) was probably accurate. It's the "doubling the output just by adding micros" claim that was the biggest puzzler no matter what what angle/view I took.

If I get anything through my (indirect) contact, I will post it here. If not, I will contact Devon to try to get info from him.
 
Last edited:
As much as this inverter would totally send my ROI into the "never paying for itself" zone and being WAY more inverter than I need today (by a lot), I'm seriously considering going this route and just being done with waiting for all the other options either coming to, or on the market, to work the bugs out, worrying about CS, TS, parts access, warranties, huge idle consumption etc. It's a BIG pill for me to $wallow, but at least it would resolve all the potential headaches and it would allow for a lot of future growth as I add an EV or two in the coming years. It's very tempting!

Anyone have a feel for when the 15k will actually be truly accessible to the folks that aren't already on a waiting list?
 
Wow, thanks to Engineer775's vid I realize how noisy the 15k can get! Mounting outdoors is starting to "sound" better ;)
That caught my attention as well! Granted I think he's videoing that in TX, basically outdoors on a warm day, so I'm sure the fans were trying to cool things down, but that was pretty loud.
 
As much as this inverter would totally send my ROI into the "never paying for itself" zone and being WAY more inverter than I need today (by a lot), I'm seriously considering going this route and just being done with waiting for all the other options either coming to, or on the market, to work the bugs out, worrying about CS, TS, parts access, warranties, huge idle consumption etc. It's a BIG pill for me to $wallow, but at least it would resolve all the potential headaches and it would allow for a lot of future growth as I add an EV or two in the coming years. It's very tempting!

Anyone have a feel for when the 15k will actually be truly accessible to the folks that aren't already on a waiting list?
EcoDirect told me they three weeks ago that they are shipping at the start of June.
 
15k video review by Engineer775:
I watched the video and it was pretty good.
I thought he answered several of the questions about AC coupled panels.

I talked to EcoDirect and from what I gather they could only get 50 units on their pre order. First batch of 25 came in and was pre-sold and is shipped. They said they have 10 units remaining from the next batch coming in on the 11th.
 
Last edited:
I've had my 15k for a few weeks now. I ordered from Alt-E. They called me to warn me that they were pre-order, and wouldn't ship until July/August. The next day I get a shipping notification. I was worried I was sent a 12k or something by mistake - nope, it's the 15K! I haven't set it up or unboxed it yet, but they are at least shipping.
 
I got a feeling that this is correct. The fact that Sol-Ark is now pushing it's own MicroInverters leads me to believe that they intend them to compliment the 15K in having a much higher capacity. I do not think they are doing it to compete directly with Enphase. I suspect they will have some sort of more in-depth communication with the Inverter that goes past just frequency shifting. I am interested to hear the info you get.
Yeah, I suspected that the pure number (20 kW) was probably accurate. It's the "doubling the output just by adding micros" claim that was the biggest puzzler no matter what what angle/view I took.

If I get anything through my (indirect) contact, I will post it here. If not, I will contact Devon to try to get info from him.

Looks like I should get some answers sometime next week.
 
Good news from Sol-Ark for people like me in California, I asked tech support if there was going to be a hardware change after the certification, or if I can buy it now, get it installed, and just wait for the certification before I get my interconnection agreement, this is his response:

For the CEC certifications, you are correct in that we do not have them yet for the 15k. This would prevent you from tying it to the grid. You can purchase the inverter and install everything other than the interconnection to the grid. There will not be a hardware change to the 15k, otherwise we would have to get CEC certifications again.
 
Clarification from solark on AC coupling the gen input:

"The gen breaker can be used for a variety of things on our inverter. You can program the gen breaker to accept AC coupled solar. When utilizing AC coupling, the inverter will provide the frequency needed to run the AC coupled inverter(s) and the power is able to feed through to the grid."

Further discussion revealed other details. The gen breaker is not bidirectional like the line and grid connections. Power will flow into the inverter from the gen connection, but will not feed out like the line and grid.
 
Clarification from solark on AC coupling the gen input:

"The gen breaker can be used for a variety of things on our inverter. You can program the gen breaker to accept AC coupled solar. When utilizing AC coupling, the inverter will provide the frequency needed to run the AC coupled inverter(s) and the power is able to feed through to the grid."

Further discussion revealed other details. The gen breaker is not bidirectional like the line and grid connections. Power will flow into the inverter from the gen connection, but will not feed out like the line and grid.

Well, at least that agrees with some of the info from Sol-Ark I referenced in posts #233 & #238. Unfortunately, it seems it is still at odds with the two Tom Brennan (Alt-E Conference) webinars which say you can use the AC coupling of micros (along with SmartLoads 14) to run your whole house if the grid goes down - which means that the panel output through the micros and into the 15K flows to the loads, right?

As far as the gen breaker not being bidirectional, that's what I assumed. I mean, if it's meant as a "generator" input (which can also take AC input from micros or an external string inverter), I thought you wouldn't want any current flowing outward towards those sources.
 
Yes, I'm guessing it sends the gen input directly to loads and/or batteries (depending on settings) in the event of grid outage.

Now in the event of inverter failure, I assume the AC coupled micros coming into the gen port become useless, even with the 200A passthrough?
 
Now in the event of inverter failure, I assume the AC coupled micros coming into the gen port become useless, even with the 200A passthrough?
The micros only become useless when the grid is down. The pass through is bidirectional so when the grid is up the micros are not actually AC coupled in the sense that they have to be controlled by the inverter to modulate their output. When the grid is up it presents an infinite load to the micros and they send all their power to the loads and the grid. I do not think the gen input is bidirectional as to current but the micros can see the voltage and test the connection for a true grid so the micros can send power to through the SolArk to the grid.
 
The micros only become useless when the grid is down. The pass through is bidirectional so when the grid is up the micros are not actually AC coupled in the sense that they have to be controlled by the inverter to modulate their output. When the grid is up it presents an infinite load to the micros and they send all their power to the loads and the grid. I do not think the gen input is bidirectional as to current but the micros can see the voltage and test the connection for a true grid so the micros can send power to through the SolArk to the grid.

Except, going back to my post #244, we have Tom Brennan, the CTO of Sol-Ark, saying in a webinar on the 15K, their new micros, & SmartLoads 14 (see the post for link to the webinar and the full discussion), that "...we can add micros to the equation and what we'll do is, we can AC couple the panels to the ESS system and we can double the output during the daytime. And that way, during the daytime, when the grid’s down, you can run everything". I added the italics. But he's clearly stating that the micros are still quite useful when the grid is down.

Again, I should get answers to these questions next week. I will push for a direct answer to this issue.
 
Clarification from solark on AC coupling the gen input:

"The gen breaker can be used for a variety of things on our inverter. You can program the gen breaker to accept AC coupled solar. When utilizing AC coupling, the inverter will provide the frequency needed to run the AC coupled inverter(s) and the power is able to feed through to the grid."

Further discussion revealed other details. The gen breaker is not bidirectional like the line and grid connections. Power will flow into the inverter from the gen connection, but will not feed out like the line and grid.
Wait can't the gen breaker be used as a smart load output?
 