Now part 2:
"
Now, I’m no EE, but I know that inverters (micro- or otherwise) cannot
create power (wattage). It can only
invert it (from DC to AC or vice versa). The only actual available sources of power for a Sol-Ark inverter are the solar panels, the grid, the batteries, or a generator. Actually there is another possible source: the output of an external inverter (with accompanying solar panels) that is AC coupled as an input to the Sol-Ark. But we’re talking about adding micros here, so the external inverter output, grid, and generator are eliminated immediately. And we’ve already said it can’t be the max 12kW (in the example of the Sol-Ark 15K) from the batteries because he’s claiming an additional 20kW (which matches the 40 x 500W solar panels). So, even if Tom is trying to show that you can get more than 15kW of solar panel wattage out of the 15K inverter by AC coupling solar panels with micros, then - if we add the (cost of the) micros only - we’re getting only a 5kW addition in output: not 20kW. If you want to get an additional 20kW, you have to include the cost of an additional 15kW of solar panels (so you have 15 kW DC coupled to the MPPT input, and 20 kW AC coupled to the gen input).
Continuing on in the same webinar, at 43:20, he has a viewgraph of a comparison of Sol-Ark with Enphase (a screenshot is attached as “Attachment 3”). In the middle of it (at 44:44, comparing the Sol-Ark 12K to Enphase) he seems to realize his mistake (because there is no doubling of wattage with micros) and stumbles a bit before trying to recover by saying you get the additional wattage during the day from
the batteries – as well as getting the same power at night. But if you consume the batteries during the day, you won’t have them available (at least for very long) at night. Then, at 46:10, comparing the Sol-Ark 15K to Enphase x 3, he does a similar pause, now claiming that the AC coupling gives a total of 32kW during the day (20kW solar + 12kW battery) and 12kW at night as well. So it seems he was having some doubts about his "doubling" math. But there’s one additional curve to throw at this analysis. I made a suggestion to a member of the DIY Solar Forum to use the capability of the Sol-Ark (12K as well as) 15K to take one set of panels he has (with micros attached) on one roof and AC couple them to the gen input of the Sol-Ark 15K, and take his other set of panels he has (without micros) on another roof and DC couple them into the MPPT inputs. His reply was as follows: “I spoke with solark (sic) about using ac coupled on the gen input and was told it is a no go. There is a setting in the battery menu to indicate if you are using ac coupled on the load side, or grid side. I was told the gen input will not flow out to the grid, so it has a problem with the sync. The inverter will sync the dc PV input to the grid, or it will sync to the gen input if a generator is running and disconnected from the grid. It will not do both at the same time. You can use ac coupled on the gen input if you are off grid, but not grid tied”. Now I know this statement to be false because I watched all 3 of Sol-Ark University’s webinars for installers (available on their website
here), and they state multiple times in all three webinars that you can simultaneously AC couple and DC couple solar panels (see screenshots from the attachments “Sol-Ark 101 screenshot”, “Sol-Ark 201 screenshot”, and “Sol-Ark 301 screenshot”). Not only that, but in the third webinar they state that the maximum combined input from solar panels from both AC and DC inputs for the 12 K inverter is 16kW (in the “Sol-Ark 301 screenshot” attachment). This latter apparent confusion could be explained if a firmware update for the 12K inverter increased the combined input to allow 18 kW (that Tom claimed in his example of doubling output for the 12K inverter). Oh yeah, one more thing: in one of those installer webinars, they state that the output of AC coupled panels always flow out to the load or the grid (directly contradicting information that the above quoted DIY Solar Forum member said that he got from his contact at Sol-Ark). In other words, you can’t use their output to charge a battery ESS.
Now, as I said in during our Zoom meeting, I am not claiming that Tom or Sol-Ark is making an intentional attempt to mislead anyone, but there sure seems to be 1) a number of claims during Tom’s webinars that he doesn’t back up with either examples or explanation (and seems to make no sense), and 2) apparent contradiction from different Sol-Ark sources, all leading to a lot of confusion. I would be very interested in any explanation your contact in Sol-Ark could provide. Many thanks for volunteering to address these issues with Sol-Ark."