The ac is a120v window unit; that's the ~1k draw on one leg. The other leg is a full size frig and small deep freeze. 240v checked with voltmeter across the legs.Is your AC 120 or 240?
What does this mean? Or how is that fixed? Sorry not trying to derail this.Imbalance on the transformer legs reduce theoretical output. Same thing happens with external auto transformers.
Thanks I'll check it out@Traviss224
Here's a victron autotransformer:
Read the part here:
"Theoretically, the total power that can be drawn from a 30A 120/240V supply is 30 x 240 = 7,2 kVA. In case of 20A unbalance, the practical maximum will be 30 x 120 + 10 x120 = 4,8kVA, or 67% of the theoretical maximum"
I know this is a different product, but the concept is the same with Low Frequency inverters
As far as we can tell, the spfxxxx units have their transformer wired as an isolation transformer in inverter mode, and autotransformer in bypass mode.@Traviss224
Here's a victron autotransformer:
Read the part here:
"Theoretically, the total power that can be drawn from a 30A 120/240V supply is 30 x 240 = 7,2 kVA. In case of 20A unbalance, the practical maximum will be 30 x 120 + 10 x120 = 4,8kVA, or 67% of the theoretical maximum"
I know this is a different product, but the concept is the same with Low Frequency inverters
I was under the impression the low freq inverters somewhat balanced their loads?
As far as we can tell, the spfxxxx units have their transformer wired as an isolation transformer in inverter mode, and autotransformer in bypass mode.
I was under the impression the low freq inverters somewhat balanced their loads?
As far as we can tell, the spfxxxx units have their transformer wired as an isolation transformer in inverter mode, and autotransformer in bypass mode.
It's not two circuits. It's a single 240/120v circuit.How is that supposed to work when they are on two separate circuits? Legit question..maybe something I'm missing about the inverters but I thought it was like the panel in our home where it was our responsibility to balance the legs.
What Tim said. For ac input, the manual states two hots and one ground, no neutral.How is that supposed to work when they are on two separate circuits? Legit question..maybe something I'm missing about the inverters but I thought it was like the panel in our home where it was our responsibility to balance the legs.
Isn't that just the input, the sticker says output is 120/240 so the only way to get that is to split the single phase with a mid way point aka neutral. I said circuit but what I meant was the two legs of the single phase. I don't think you can have one leg balance to the other leg auto magically like that...again unless there's something I'm missing. David poz did a video on this about the solark being very finicky about being out of balance. I asked here on this forum and was told you still have to manually balance your loads.What Tim said. For ac input, the manual states two hots and one ground, no neutral.
@BradCagle Working a lot of overtime this week but when time allows, I'll see what is laying around that can be used to load down the inverter ac output legs and how it reacts.
This is completely off grid. No grid input.
David Poz proved that a split-phase high frequency inverter (like Sol-Ark) is limited to separate ratings for each leg. This is a low frequency inverter. High frequency split-phase inverters are just two 120v inverters in one unit.Isn't that just the input, the sticker says output is 120/240 so the only way to get that is to split the single phase with a mid way point aka neutral. I said circuit but what I meant was the two legs of the single phase. I don't think you can have one leg balance to the other leg auto magically like that...again unless there's something I'm missing. David poz did a video on this about the solark being very finicky about being out of balance. I asked here on this forum and was told you still have to manually balance your loads.
Ok, thanks for that. But, lets say that the inverter did have the capabilities internally to balance L1/L2 but you had a case where you had various things plugged into the same leg down stream and the inverter started to pull from the other leg to balance it internally but it still has to push that current all out the same leg those appliances are attached to? Wouldn't that cause a potential over load situation and fire risk? Interesting topic...I'm intrigued to learn more about this.David Poz proved that a split-phase high frequency inverter (like Sol-Ark) is limited to separate ratings for each leg. This is a low frequency inverter. High frequency split-phase inverters are just two 120v inverters in one unit.
The inverter doesn't balance anything. The transformer does it. It's still best to balance the loads as best you can. But, you're not limited to only half per leg.Ok, thanks for that. But, lets say that the inverter did have the capabilities internally to balance L1/L2 but you had a case where you had various things plugged into the same leg down stream and the inverter started to pull from the other leg to balance it internally but it still has to push that current all out the same leg those appliances are attached to? Wouldn't that cause a potential over load situation and fire risk? Interesting topic...I'm intrigued to learn more about this.
Ah, ok I got what you're saying now.The inverter doesn't balance anything. The transformer does it. It's still best to balance the loads as best you can. But, you're not limited to only half per leg.