Then you would lose any benefit of have the BMS. For a 4S pack the BMS should be able to balance even those cells. Or help it along with a resistor or 12 volt bulb on the high cell.I'd have to unplug the BMS balancing cables to disable it since the apps don't give me any useful control.
Yes. As long as the cells are good any amount of imbalance will be corrected over time.A 5A capacitor(12 caps) active balancer would work with a 280K 4S set up with a .029 delta imbalance?
29mV delta V at pack voltage 14.2V would be regarded as approaching balanced.A 5A capacitor(12 caps) active balancer would work with a 280K 4S set up with a .029 delta imbalance
Depends on the settings. Most recommend balance only while charging. This is a more constant way to ensure all are similar state of charge condition.Does the BMS continue to balance when the battery is not being charged?
Is the JK BMS you are using the one you have to "jump start" with a 9v battery the first time it is connected? I have 2 of those I will be hooking up in a week or so and wondered how the 9v "Jump Start" thing might effect the project long term. How often would it need to be "Jump Started"? At LVC? Seems an odd way to design a BMSI decided to abandon the Chargery Setup (300 USD) & QNBBM-8 ((150 USD) for 5 packs in favour of the JKBMS because it's all in one Nice Tidy Package and no issues. In fact, the whole setup in my parallel bank works amazingly well (better than I hoped for actually).
I still have not heard from them !!
I have been experimenting over the last month and have found that using a normal JBD bms and hooking up a Heltec 5A active balancer is not only cheaper but works soooo much better than JK !! I had a pack with a JK and it would never ever actually balance or get close but after installing the Heltec and giving it a few days the pack is now balanced and stays balanced ! The JK could not even come close to it in performance!!
I have give up on JK BMS's they are not worth the trouble! I know they sound like they should be good but when you put them to the real test they can't pull their weight anyway let alone the BACKUP SERVICE that DOESN'T EXIST! when they fail!
I saw another user @Alltron have success with Active Balancer with JBD BMS.
I was curious on a few things.
1 - Do you turn off either of the balancing features in the JDB app?
2 - I saw a interesting YT video from Off Grid Garage where he tested that it may not be good to keep Active Balancers on all the time.
Reason is it may also unbalance during lower state of charges.
3 - Also heard about installing a switch on the Active Balance to do it only when needed or there may believe be a way to automate this further somehow by wiring it up to kick in at higher SOC or volts.
Thoughts, Tips and More Info from any experts on this to set us Noobs straight? lol
Thank you!
Gette,
Take a look at this message in a previous thread on active balancers. This setup has worked well for my JBD BMS's with active balancers. The JBD (Overkill Solar BMS's) are also set to balance on any cell with a voltage above 3.4 volts only.
Active balancer or not?
this: Testing 3 battery banks with and without active balancer ... is great info. for this thread. ... has convinced me using active balancer at only the higher charge voltages ...like >3.4 v ... Is a Very Good Idea. OK and the solar voltage is set to 55.2 and apparently causes no issue...diysolarforum.com
Also checkout the link to Overkill Solar downloads and download the user manual. It is very well written for the JBD BMS
Support/Downloads
User Manual User Manual: Download Manual (6.5mb PDF) Simplified 4 Cell Assembly Ultra simple view of a complete 4 cell battery assembly. – Click for full resolution. Bluetooth Mobile Apps iPh…overkillsolar.com