Goodmorning to you all !

A SOK battery 206AH and a Maximum Continuous Discharge Current of 100AH put in parallel connection, will the Maximum Continuous Discharge Current become 200 AH ore just stay 100 AH ? the marine version better i you want to put them in series connection ?

Thanks for any respons.
 
When put in series, the voltage adds up. And amperage stays the same.
When put in parallel, the amperage adds up. And voltage stays the same.
 
  • Like
Reactions: RJR
Maximum Continuous Discharge Current ?
People start calculating how many amps they can pull continuously like this and then get disappointed when a BMS disconnects on them because of a situation that caused one of the BMS to get hit by a 100A load, which can still shut them down...

If you're pulling a lot of amps, don't skimp on usage of busbars, use equal wire lengths, high quality wire/crimping, etc (read Victron Wiring Unlimited, you don't have to spend anything to do it). Understanding current sharing is important or following a design that manages this issue.

But yes in a perfect design the loads would distribute nearly evenly between the two battery packs, so that they would not hit their 100A limit until you pull around 200A total.

EDIT: I design my systems to use less than half the "max", more like a third... those MAX specs will help you handle surges like motor startup inrush currents that you didn't know exist. If you use nearly 200A@51V from 2 batteries sustained or often I doubt it will go well.
 
  • Like
Reactions: RJR
Agreed
Maximum discharge should only be factored for surges.
Unless you really expect to only need power for an hour. And only need that a few times a month.
Otherwise plan on less than half, for longevity.
I usually run less than 15%.
 