Not to happy with Magnum.

I only can say that on my MS2812, the display shows 'inverting' and shows how many amps draw on the battery side (I can only run one of my roof air conditioner units while inverting, since it's a 2800w inverter), then when I start the generator and the AC power input kicks on, the 'inverting' on the display goes away, then says Absorption, or Float charge or something (while amps indicates amps charging on battery), and the reason I know it is in bypass, is because while in this mode I can run both roof air conditioner units at same time (since my genset is an Onan 6300w), and when I turn them on I can hear them bog down the generator for a second until they stabilize. I am not manually flipping any bypass switch or anything. The Magnum just acts like an ATS in that sense. It uses the same mosfets for inverting and battery charging (like so many inverters), that it cannot do both at the same time.
Sounds just like when I had the 4024. Never did use the 4448 charger but one time and it did the same. I’m going to have to read the instructions again. But on the 4024 we never used the bypass nor has the people before or after me. Neither house has any large loads. My biggest load now is a 5k 120v window air.
 
the inverter and design are the same magnum has been using for over a decade, its not like it has went up or down, its magnum's lack of response to end users that has went down. the 4448 works the same as my 2012 (and I am postulating the same as any other of the MS series) when it receives and quantifies that shore power is stable will then bypass the inverter side, pass through current to the end load (house) and then attempt to charge. if your settings are incorrect and or your genset too small to power both simultaneously then it will fall in and out. this is what is bad for the charge control board the fluctuations are not good for it.

this is one of those things where you need to ensure that the capacity fo the genset is sufficient that or turn down the total allowed power for charging purposes both input amps and percentage until you find the correct balance.

EG: If I use my makita genset its max output is 18 amps at 240. I allow the charging side 8 amps and set max charge at 40% and everything is good to go if my house suddenly draws more than 10 amps on either leg then the genset will stumble and charging will stop until power stabilizes again.

love the inverter... hate Sensata. (nee magnum)
 
Both my 4024 and 4448 have separate bypass breakers and will charge while inverting.
I think that you really need to reread the Magnum manuals.....They cannot charge and invert at the same time. The bypass breakers in the control box only bypass the inverter for servicing.

The same transformer and logic board are used for both charging and inverting.

It is physically impossible for it to charge and invert at the same time.

It can charge battery and bypass power from input to output at the same time

That IS NOT charging and inverting at the same time


When it is inverting it is disconnected from the AC input but the bypass relay in the inverter itself can and does bypass power from AC input to AC output.

I do have a MagnaSine MS4024 AE which can and does run on 120 volt only and will output 120/240 through its main transformer whose primary circuit is “Autotransformer”

I can and do use my Magnum MS4024 with a Onan 6 kw. 120 volt generator and it does provide 120/240 volt split phase output when in charge mode.

The Split Phase Magnums, MS4024AE, MS4024PAE, MS4048AE, and the MS4048PAE all have “autotransformers“ as the main transformers and can and do output split phase from a single phase input as do some other brand “Split-phase” units which includes some Schneider and Outback (Radian) units.

The “AE” and “PAE” models can only accept input on L1 in single phase. Single phase input on L2 wii not be recognized as L1 is checked first. If L1 is not 120 volts then L2 is checked for being 120 volts AND 180 degrees out of phase with L1....... For 240 volt input it “MUST BE” 120/240 split phase and NOT...240 volts.....(not split phase).....OR.....120 volts from two different generators....OR......two legs of a three phase generator
 
Last edited:
I have been using Magnum units for quite a number of years now but I would not buy another one directly due to Sensata failing to support the Magnum brand. My MS4024AE is still working fine but I have a freinds MS2000 on my bench which works fins at small loads with good effeciency but when loaded up to 1500 watts emits burning smell and blows 300 amp ANL fuse.

It did this in a van camper using two Battle Born 100 a.h. batteries and does the same thing on my test bench using 4 Rolls-Surette L-16 batteries in series/parallel (842 a.h.)

No response from Magnum....

It emits “burnt component stink“ but nothing gets hot.....Using Fluke 62 Max IR thermometer nothing gets to 100 deg. F except what appears to be a voltage regulator chip on the control board. The Main FET’s do not get hot.....80 deg. F in California is nothing to be concerned about.

My freind bought another MS2000 but it is “OLD STOCK” as it is not the current version MS-2000-L as he was in a hurry to get the van camper ready for a field trip.

I had recommended the Victron but it would not fit in the place of the Magnum unit.
 
After another day of phone calls I did get some results. Not what I wanted but working in the right direction. Spoke with a guy that says he was in the inner circle while Sensata was making bad decisions. He claims they are not going out of business. They are in the process of moving to Warrez Mexico. They do source parts from China when they can. They were supposed to run the production plant in the USA until the Mexico plant was up and running. But all the employees quit. So they had to shut down to focus on the Mexico plant. They do plan on reopening a repair facility in the US when that start getting more parts.

He also confirmed what was wrong with my unit and sold me the parts to fix it myself. He told me to hold onto the invoice and when magnum is back up and running to ask them for a refund.
 
Good that you got a human and some parts.. but why would any reseller be selling one of these now?
 
Good that you got a human and some parts.. but why would any reseller be selling one of these now?
Most everyone I spoke with other then this guy has sold what stock they have and claim they will no longer be dealers for them. One company that was an authorized repair shop even threw away 12 parts inverts.
 
This sad to hear. I’ve been out of the loop for a few years. I’ve always believed that magnum was a fantastic product, and even better support. I expect nothing less for the price charged. (Price, quality, service… pick 2).

magnum is 3x the other stuff. But it sounds like they want the quality and service of “lower” products but want to charge the premium price?
 
According to the Magnum support guy, on the MS-4024/4448-PAE Hot-In-1 is charge leg and Hot-In-2 is pass thru. This seems to support the fact that it can't charge and invert at the same time. I do like the bypass feature; it allowed me to replace my batteries while the generator provided power and lights.

The manual does state that if you are not using the 2nd AC leg input, that you must turn down the charging rate to 50% or you'll damage the unit. I'm just worried that if one leg of the generator trips a breaker, it will kill itself but so far, then the generator trips, it has tripped both breakers so maybe this is how it is supposed to work. I am tempted to put a DPDT breaker to make sure it never provides power on only one leg. But then again, if the inverter/charger works as above, it shouldn't be an issue. Hmmm, if the inverter passes power thru when it charges the batteries, does this mean I need to worry about my generator providing clean (pure sine) power for my home? Why are some generators also "inverters"?

My unit had an electrical burn-in smell for about 6 months of charging 6hrs twice a week at max current. It has finally quit stinking.
 
You have very bad information as to how the Magnum MS series is wired and works. Not if and or but.

SOME Victron units do use L1 for charge or passthrough and L2 for passthrough only but these are 120 volt units that can power from 120 volts or 240 volts. The inverter is 120 volts ONLY

The Magnum MS series can either invert or battery charge. It can operate at reduced power charging or pass-thru with 120 volts only , but cannot charge and invert at the same time. That does not matter if you are using 120 volts or 120/240 volts as power input

If you are charging using only Leg 1 input you need to turn the current limit down to 45 amps to prevent damage to the main transformer

You must turn the charge current down when using Leg 1 only but as the Magnum MS series DOES employ an autotransformer as the main transformer you are limited to 2900 watts throughput when only 1 input is used.

Unlike other units which do not use an autotransformer you can energise only leg 1 input with 120 volts but you can get 240 volt output from leg 1 and leg 2 BECAUSE it is an autotransformer.

Schneider Electric does this in their XW series, I’ve not worked on them all, only some models, but for sure the XW-4024, XW-4048, and XW-6848 are wired with autotransformer, I have expereince with all these inverters along with many others MADE IN AMERICA.......

I do have a Magnasine MS-4024AE.......the predecessor of the MS-4024PAE and MS-4048PAE, been using it for 20 years in that configuration. My POCO feed is 30 amps, 120 volts from 1929......I do rarely charge my batteries from the POCO feed My shop is 120/240 split phase but my house is 120 volts only.

I do have more than one Magnum inverter but they are not the same voltage...a MS2012, a 12 volt RV inverter

I’m 99.995% off grid solar but by state law I must be connected to the grid to have and retain my certificate of occupancy.......I use about $5.00/month from Pigs,Goats,&Elephants, PG&E to you, our local power company

Atteched please review the primary schematic of the MS-XXXX-PAE and AE units.
This is in the Magnum manual
 

Attachments

  • C9489520-FFE0-476E-897A-FC881C689F88.png
    C9489520-FFE0-476E-897A-FC881C689F88.png
    147.2 KB · Views: 6
Last edited:
The schematic shows the unit in invert mode, note the AC input relay is in the off mode (Invert) and the AC line input is disconnected from the transformer.

ALL.....the AMERICAN......units that are low frequency that I have worked on do use the same electronics (FET’S) ,transformers, etc. for both the inverter and battery charger, It’s all the same parts, just phase angle’s of the FET’s are changed from invert to charge mode. It is impossible to charge and invert at the same time.

Please dont ask me about Chinese stuff......I did a career in American High Tech, I cant get the Chinese stuff to be reliable......

I still have and use a DYNAMOTE BRUTUS, the very first high frequency electronics driving a low frequency transformer inverter. It is an inverter only, it does not have the capability to charge batteries. Predates the Legendary Trace units that still work after so many, many years.
 
Last edited:
Its a bummer they are going through some changes and I hope they come back. I have a MS 2812 and a spare. Nice inverter. Got them in a trade. I abuse it and it just keeps going. Only pulls 30w idle. I would not buy one in the future though and I'm buying some 24v and 48v inverters. I'm only buying Victron going forward. At least till they die....lol
 
Samlex is very impressive, rock solid unit as far as I have seen, they too are low frequency iron core transformers.
I have never used their inverters but I do have Samlex DC-DC Converters , both the SDC-30 non-isolated and the IDC-30 fully isolated converters and have never had a bit of trouble with them. The inverters are built in America but the dc-dc converters are from Holland, if I remember correctly. One of the volunteers on the forum has Samlex inverters and is really happy with them.

I would not buy another Magnum directly due to the service/parts situation......but I’m spoiled, waiting for my Midnight inverter , if they release the Rosie in a 24 volt configuration, was set up to beta test these but Im 24 volts, works for me, but if I were to start from scratch I would go 48 volts
 
BEFORE.....you buy, research tech support from Victron and Samlex....I did...not impressed with Victron support, Samlex is there.

Tech support is exactly why I bought Midnight.....I called them all, mostly you will get script readers, at Midnight if you ask a though question you get a very knowledgeable tech support, I got @SpongeboB Sinewave , very reassuring if you are going to spend bucks for something that will be life supporting.
 
BEFORE.....you buy, research tech support from Victron and Samlex....I did...not impressed with Victron support, Samlex is there.

Tech support is exactly why I bought Midnight.....I called them all, mostly you will get script readers, at Midnight if you ask a though question you get a very knowledgeable tech support, I got @SpongeboB Sinewave , very reassuring if you are going to spend bucks for something that will be life supporting.
I have seen the Samlex units. They look good. How is the idle power? Do they have a good app for their inverters?
 
I have heard idle power is 18 watts, for the 4 kw. unit. I believe that it is XXXXXX (edited) who uses Samlex inverters, Too much data in computers overloaded at the moment


EDIT.......BAD DATA......NOT Supervstech using Samlex. it’s ..@Steve_S who has a Samlex EVO
 
Last edited:
On a side note, one thing I don't like about my Magnum's internal charger function, is when I start the generator to charge, the inverter section automatically goes into bypass, so then the generator has to run all the normal output loads + the charger too (requires bigger generator which can meet both demands).

My most recent solution is to just use two standalone chargers to charge the batteries directly from generator, so the inverter will stay on like normal, and charge that way, alongside.

I will also be doing this with my final home 48v system too, since the MPP Solar LV6548 all-in-ones I have also must go into bypass mode in order to charge the batteries from AC input (is not able to charge while 'inverting'). So I bought 2 AIMS 120v 48v chargers to wire in, one on each leg of generator, so i can just add supplemental charging on my own circuit to the batteries.

Perhaps at worse case, you could just buy some 48v chargers and add them in and not use the AC input on the 4448 at all. Or so you can just buy some time and fix it later...
All hybrid inverters have inverter-charger connected to AC output. When AC input is detected, and before AC pass-through relay closes, the inverter is slowly brought into phase alignment and AC input voltage matching. Once this is achieved the pass-through relay closes and AC input is passed through to AC output with inverter-charger in parallel.

The difference is if hybrid inverter allows load shaving of AC input. Some low cost LF hybrid inverters and most HF hybrid inverters do not do AC input load shaving. If it does not do load shaving then AC input provides AC charging and AC output power with no control on maximum generator loading.

LF hybrid inverter are inherently bi-directional so it is very easy for them to do load shaving. HF inverters are not inherently bi-directional and have to switch forward/reverse power operating modes that takes several milliseconds to switch between. This restricts HF hybrid inverter from load shaving unless they have a large bank of high voltage storage capacitors to provide load power while battery to HV DC converter is temporarily inactive making its forward/reverse power direction switching.

On Magnum inverters, they call load shaving 'Shore Max' which is a user set limit for AC input current.

From Magnum manual:
Shore Max - This setting ensures the inverter AC loads receive the maximum current available
from the utility or generator power. When the total current used to power the AC loads and charge
the batteries begins to approach the Shore Max setting, the current that was used for charging
the batteries will automatically be reduced.


This means AC output has first priority on limited AC input current.

Usually, a LF hybrid inverter with load shaving will allow battery power to supplement AC input power to allow AC output load greater than generator capability. I am not sure if Magnum does this. Victron, Xantrex, and Outback units do allow this.

The most common issues with AC input from a generator:

1) Generator out of freq range (synchronous constant rpm generator)

2) Too much rpm wobble due to unstable generator engine governor rpm control preventing inverter from achieving phase lock (synchronous constant rpm generator). Generator sound should be smooth and constant, without any 'wah-wah' sound pitch variance. Frequency accept range limits is not the same as frequency lock wobble range. Lock for inverter requires generator frequency wobble less than about +/- 0.3 Hz around AC frequency (50 or 60 Hz).

A sudden surge load on a synchronous fixed rpm generator can cause rpm variance dip causing inverter to release from generator. This is where AC output supplementing from battery power through inverter really helps prevent generator from seeing a sudden AC output surge, like an AC motor startup. Victron takes this a step further with their dynamic load shaving where the inverter begins to supplement AC output load that starts to quickly rise before it has actually reaches the AC input current limit set by user. It backs down the supplementing by battery when AC output load settles out.

3) If inverter has AC input current limiting (load shaving), not set properly for generator power capability resulting in overloading generator. Inverter will connect to generator then quickly disconnect from generator when generator bogs down from overload. Inverter may wait some time period and try to reconnect again.

4) If inverter does not have load shaving, setting charger at a level that exceeds power capability of generator, again overloading generator.,

First thing to listen for is pass-through relay engaging indicating inverter has achieved lock on generator. Many inverters also have an indicator LED. This can take from about 10 seconds to upward of a minute or two depending how much initial frequency difference between generator and inverter.

Inverters that have two AC input options often have the AC input used primarily for grid connection set to a tighter AC input frequency range that may not cover the actual frequency of a synchronous, constant rpm generator, therefore the inverter may not lock to a generator out of the tighter frequency limit range.

For inverter-generators, the frequency and its stability is usually very good, but they can react very quickly to overload by shutting down their AC output. When using ECO mode, where rpm is reduced, sudden load increase causes output sinewave to be peak clipped until engine rpm comes up to higher rpm's to meet the higher load demand. Usually, the inverter will step up to supply the additional sudden load until inverter-generator comes up to speed, so the inverter does not release from inverter-generator.

For a LF 240/120 vac inverters that allows just a 120 vac input it is important to remember the AC input current load shaving limits is only providing half the power that a 240 vac input would supply.
 
All hybrid inverters have inverter-charger connected to AC output. When AC input is detected, and before AC pass-through relay closes, the inverter is slowly brought into phase alignment and AC input voltage matching. Once this is achieved the pass-through relay closes and AC input is passed through to AC output with inverter-charger in parallel.

The difference is if hybrid inverter allows load shaving of AC input. Some low cost LF hybrid inverters and most HF hybrid inverters do not do AC input load shaving. If it does not do load shaving then AC input provides AC charging and AC output power with no control on maximum generator loading.

LF hybrid inverter are inherently bi-directional so it is very easy for them to do load shaving. HF inverters are not inherently bi-directional and have to switch forward/reverse power operating modes that takes several milliseconds to switch between. This restricts HF hybrid inverter from load shaving unless they have a large bank of high voltage storage capacitors to provide load power while battery to HV DC converter is temporarily inactive making its forward/reverse power direction switching.

On Magnum inverters, they call load shaving 'Shore Max' which is a user set limit for AC input current.

From Magnum manual:
Shore Max - This setting ensures the inverter AC loads receive the maximum current available
from the utility or generator power. When the total current used to power the AC loads and charge
the batteries begins to approach the Shore Max setting, the current that was used for charging
the batteries will automatically be reduced.


This means AC output has first priority on limited AC input current.

Usually, a LF hybrid inverter with load shaving will allow battery power to supplement AC input power to allow AC output load greater than generator capability. I am not sure if Magnum does this. Victron, Xantrex, and Outback units do allow this.

The most common issues with AC input from a generator:

1) Generator out of freq range (synchronous constant rpm generator)

2) Too much rpm wobble due to unstable generator engine governor rpm control preventing inverter from achieving phase lock (synchronous constant rpm generator). Generator sound should be smooth and constant, without any 'wah-wah' sound pitch variance. Frequency accept range limits is not the same as frequency lock wobble range. Lock for inverter requires generator frequency wobble less than about +/- 0.3 Hz around AC frequency (50 or 60 Hz).

A sudden surge load on a synchronous fixed rpm generator can cause rpm variance dip causing inverter to release from generator. This is where AC output supplementing from battery power through inverter really helps prevent generator from seeing a sudden AC output surge, like an AC motor startup. Victron takes this a step further with their dynamic load shaving where the inverter begins to supplement AC output load that starts to quickly rise before it has actually reaches the AC input current limit set by user. It backs down the supplementing by battery when AC output load settles out.

3) If inverter has AC input current limiting (load shaving), not set properly for generator power capability resulting in overloading generator. Inverter will connect to generator then quickly disconnect from generator when generator bogs down from overload. Inverter may wait some time period and try to reconnect again.

4) If inverter does not have load shaving, setting charger at a level that exceeds power capability of generator, again overloading generator.,

First thing to listen for is pass-through relay engaging indicating inverter has achieved lock on generator. Many inverters also have an indicator LED. This can take from about 10 seconds to upward of a minute or two depending how much initial frequency difference between generator and inverter.

Inverters that have two AC input options often have the AC input used primarily for grid connection set to a tighter AC input frequency range that may not cover the actual frequency of a synchronous, constant rpm generator, therefore the inverter may not lock to a generator out of the tighter frequency limit range.

For inverter-generators, the frequency and its stability is usually very good, but they can react very quickly to overload by shutting down their AC output. When using ECO mode, where rpm is reduced, sudden load increase causes output sinewave to be peak clipped until engine rpm comes up to higher rpm's to meet the higher load demand. Usually, the inverter will step up to supply the additional sudden load until inverter-generator comes up to speed, so the inverter does not release from inverter-generator.

For a LF 240/120 vac inverters that allows just a 120 vac input it is important to remember the AC input current load shaving limits is only providing half the power that a 240 vac input would supply.

Right on, as usual... Just a couple of additions...

"LF hybrid inverter are inherently bi-directional so it is very easy for them to do load shaving. HF inverters are not inherently bi-directional and have to switch forward/reverse power operating modes that takes several milliseconds to switch between. "

A HF inverter/charger certainly CAN be bi-directional but most are not... Or at least did not used to be the case for Chinese hybrids like the MPP Solar...

The MidNite Rosie is a HF bi-directional inverter/charger that also does generator and grid support from battery.

I thought that the Sol-Ark (Deye) inverter was full bi-directional ? Uses IGBTs on the HV side. Maybe you said it was not bi-directional but I may not have been complete enough in my analysis ?

"On Magnum inverters, they call load shaving 'Shore Max' which is a user set limit for AC input current."

The other term for this is Back-off which reduces charging based on AC input current settings so you don't trip the AC input breaker as well as over-current the bypass relay contact ratings.

Also, the Magnum charger is a PFC charger that uses the same hardware as the inverter but uses a dedicated PFC IC and leakage inductance of the big transformer. I don't think there is a time penalty when going from charging to inverting ? It has been many years.

boB
 
I have heard idle power is 18 watts, for the 4 kw. unit. I believe that it is XXXXXX (edited) who uses Samlex inverters, Too much data in computers overloaded at the moment


EDIT.......BAD DATA......NOT Supervstech using Samlex. it’s ..@Steve_S who has a Samlex EVO
My Magnum 4024 when inv is on= 31W.
 
My Magnum 4024 when inv is on= 31W.
Just curious....which model 4024 do you have, mine is a very early MS-4024AE which is 120/240 but unlike the load shaving/load sharing that the PAE has it does not load share, Inverter on with no load 40 watts but the thermal fan controller is broke so the fans do not turn off. Home built thermal controller added which senses current and temperature idle power is 22 watts , not temp or load triggered

I have no complaints whatsoever, bought it used with the stuck fan control for $200 more than 20 years ago and spent some time and a few bucks to do variable speed fans, whats a retired power engineer to do?
I hope that Midnight does a 24 volt Rosie....
 
A HF inverter/charger certainly CAN be bi-directional but most are not... Or at least did not used to be the case for Chinese hybrids like the MPP Solar...

The MidNite Rosie is a HF bi-directional inverter/charger that also does generator and grid support from battery.

I thought that the Sol-Ark (Deye) inverter was full bi-directional ? Uses IGBTs on the HV side. Maybe you said it was not bi-directional but I may not have been complete enough in my analysis ?
I said they require a large HV DC capacitor bank to ride through the temporarily inactive battery to HV DC converter when it is making power flow direction changeover if they support load shaving. If doing battery charging and all of sudden needs to supplement AC output for load shaving it has to immediately go from charging to sourcing.

Yes, it is possible to make a true bidirectional HF DC to DC converter, but you will take a sizable hit on conversion efficiency.

This is the HV DC capacitor bank in the Deye HF inverter, which is pretty much same as SolArk. Each capacitor is 1000 uF @ 315 wvdc rating.

Deye HV DC filter.jpg

Typical low-cost HF hybrid inverter MPP manufacturer knockoff has just two 500 uF capacitors for their HV DC bus. Not enough to ride through mode changeover of HF battery DC to HV DC converter for load shaving without a sizable voltage glitch.

MPP PIP5048 board HV caps.jpg
 
Last edited:
Just curious....which model 4024 do you have, mine is a very early MS-4024AE which is 120/240 but unlike the load shaving/load sharing that the PAE has it does not load share, Inverter on with no load 40 watts but the thermal fan controller is broke so the fans do not turn off. Home built thermal controller added which senses current and temperature idle power is 22 watts , not temp or load triggered

I have no complaints whatsoever, bought it used with the stuck fan control for $200 more than 20 years ago and spent some time and a few bucks to do variable speed fans, whats a retired power engineer to do?
I hope that Midnight does a 24 volt Rosie....
MS4024. Specs say 25W.
 
Just curious....which model 4024 do you have, mine is a very early MS-4024AE which is 120/240 but unlike the load shaving/load sharing that the PAE has it does not load share, Inverter on with no load 40 watts but the thermal fan controller is broke so the fans do not turn off. Home built thermal controller added which senses current and temperature idle power is 22 watts , not temp or load triggered

I have no complaints whatsoever, bought it used with the stuck fan control for $200 more than 20 years ago and spent some time and a few bucks to do variable speed fans, whats a retired power engineer to do?
I hope that Midnight does a 24 volt Rosie....

One of the first things I did when at Magnum was to reduce the idle of their new line of RE SW inverters. It was like, 45 or 50 watts. 30W or so was about as low as it could get as I remember

boB
 
I said they require a large HV DC capacitor bank to ride through the temporarily inactive battery to HV DC converter when it is making power flow direction changeover if they support load shaving. If doing battery charging and all of sudden needs to supplement AC output for load shaving it has to immediately go from charging to sourcing.

Yes, it is possible to make a true bidirectional HF DC to DC converter, but you will take a sizable hit on conversion efficiency.

This is the HV DC capacitor bank in the Deye HF inverter, which is pretty much same as SolArk. Each capacitor is 1000 uF @ 315 wvdc rating.

View attachment 143096

Typical low-cost HF hybrid inverter MPP manufacturer knockoff has just two 500 uF capacitors for their HV DC bus. Not enough to ride through mode changeover of HF battery DC to HV DC converter for load shaving without a sizable voltage glitch.

View attachment 143097

"Yes, it is possible to make a true bidirectional HF DC to DC converter, but you will take a sizable hit on conversion efficiency."

How much of a hit in efficiency do you think that adds ? There are always compromises and tradeoffs.

I think it costs less to just use a synchronous design these days if it is going to be a HF inverter/charger.

Sync rectifier shouldn't add a hit to inverter efficiency (much?) but nobody cares about charging efficiency. Or very few these days.

boB
 
One of the first things I did when at Magnum was to reduce the idle of their new line of RE SW inverters. It was like, 45 or 50 watts. 30W or so was about as low as it could get as I remember

boB
boB,

I was mixing my inverters, the 22 watts is the very old Exeltech XP-1100 which does not have the low idle kit, The Magnasine idles at 40 watts cold but 58 watts after its been hot for a while with the fans running at full speed.

I’m super energy effecient as I normally use the Exeltech inverters as they are much quieter than the Magnasine both audible noise but more importantly (to me) very low EMI/RFI

I can easily do with my newer Exeltech XP-600 at night as all my lighting and refrigeration , communications, computing , routers etc. are DC..