Inherited an old 12V lead acid system and ended up changing the batteries/inverter/solar panel controller. Still 12V, but now with four 206ah SOK LiFePO4 wired in parallel to a DC fuse box for the lighting, water heater and water pump; a victron mppt; and a 3000w inverter (pure sine wave) for the additional AC load.

I have two questions:
1) I have the copper ground from the old battery bank attached to the new bank, but the solar panels are grounded and am wondering if that is too many grounds?
2) Will 4/0 be overkill for recabling the DC house fuse to battery bank, the inverter to bank and the controller to bank? All the cables will be 5ft or under in length. The current cables are degrading/old and too long. I have 2awg within the battery bank.
 
Last edited:
1) I have the copper ground from the old battery bank attached to the new bank, but the solar panels are grounded and am wondering if that is too many grounds?
Are the solar panels grounded to their own rod or is there a wire running all the way back to the main breaker box?
2) Will 4/0 be overkill for recabling the DC house fuse to battery bank, the inverter to bank and the controller to bank? All the cables will be 5ft or under in length. The current cables are degrading/old and too long. I have 2awg within the battery bank.

What's the maximum draw of all the equipment added up? 2/0 is plenty up to 200a which is all any individual battery can do so I would say that 4/0 is not excessive overkill. 2AWG was only good up to about 120a so sizing up now is probably a good idea.
 
Are the solar panels grounded to their own rod or is there a wire running all the way back to the main breaker box?


What's the maximum draw of all the equipment added up? 2/0 is plenty up to 200a which is all any individual battery can do so I would say that 4/0 is not excessive overkill. 2AWG was only good up to about 120a so sizing up now is probably a good idea.
Thank you for your reply. The solar panels are grounded to their own rod.

I've no idea the max draw. I am working on upgrading the system that came with the house as I live remotely and supplies/services are not readily available, so I upgraded the batteries based on what had been there. On the AC side, the inverter is mainly used as a charger for laptops, phones, vacuum, tools and the only long draw is an air purifier during fire season. The DC side is lights, hot water heater, RV water pump, a couple of fans and the long draw would be another external water pump when I need to transfer water.
 
Are the solar panels grounded to their own rod or is there a wire running all the way back to the main breaker box?


What's the maximum draw of all the equipment added up? 2/0 is plenty up to 200a which is all any individual battery can do so I would say that 4/0 is not excessive overkill. 2AWG was only good up to about 120a so sizing up now is probably a good idea.

Oh and if I'm upgrading the wire to the DC fuse box, there's a T class fuse (110a) which I'm guessing I'll be switching out as well to 250a (195x1.25)?
 
Last edited:
Oh and if I'm upgrading the wire to the DC fuse box, there's a T class fuse (110a) which I'm guessing I'll be switching out as well to 250a (195x1.25)?
Yes. In a perfect world you'd have 2 fuses, 1 for each 24v bank of batteries but your math is correct.
 
If you identify the solar panels, via their label on the back of one, you can then dig up online the installation guide for it. This might tell you how the panel (frames) should be grounded. My guess is that the panel frames are separately grounded for lightning protection.

Everywhere else, there should be only one ground (multiple bonded points to one ground are the same as one ground), and this is usually at or near the AC breaker panel.

As (I believe) you have a mixed system, and how that was wired may not have been discovered yet, I'd still follow the rule of "one ground" for the house wiring, such as it is. The sooner you discover/review all the wiring, the better ... who knows what other fun things are in there. If you do find multiple ground rods or such, then that can be puzzled out, depending on how the wiring got done.

A local electrician would know the rules of NEC code (or whatever applies) and your area, and would be able to review the grounding setup you've got, and test it's effectiveness. Because you are remote, you may have to do the legwork yourself, draw it up a bit, and run it past someone, who may not otherwise come out to where you are. I think it's very worthwhile to have a diagram of what you've got anyway ...

Adding this section to differentiate: "System Grounding vs. Equipment Grounding"
- System grounding is the intentional connection of a current carrying conductor to earth ground. In U.S. homes, the neutral conductor bonds to ground in one location (typically in the main service panel). On PV systems, traditionally, the DC negative bonds to ground but is often done internally to the equipment and isn’t always a direct connection (thus, identify what components you have, get the install guides).
- Equipment grounding bonds all non-current-carrying metal parts to ground. In a PV system, this includes racking, solar panel frames and equipment enclosures.

Hope this helps ...
 
Last edited:
If you identify the solar panels, via their label on the back of one, you can then dig up online the installation guide for it. This might tell you how the panel (frames) should be grounded. My guess is that the panel frames are separately grounded for lightning protection.

Everywhere else, there should be only one ground (multiple bonded points to one ground are the same as one ground), and this is usually at or near the AC breaker panel.

As (I believe) you have a mixed system, and how that was wired may not have been discovered yet, I'd still follow the rule of "one ground" for the house wiring, such as it is. The sooner you discover/review all the wiring, the better ... who knows what other fun things are in there. If you do find multiple ground rods or such, then that can be puzzled out, depending on how the wiring got done.

A local electrician would know the rules of NEC code (or whatever applies) and your area, and would be able to review the grounding setup you've got, and test it's effectiveness. Because you are remote, you may have to do the legwork yourself, draw it up a bit, and run it past someone, who may not otherwise come out to where you are. I think it's very worthwhile to have a diagram of what you've got anyway ...

Adding this section to differentiate: "System Grounding vs. Equipment Grounding"
- System grounding is the intentional connection of a current carrying conductor to earth ground. In U.S. homes, the neutral conductor bonds to ground in one location (typically in the main service panel). On PV systems, traditionally, the DC negative bonds to ground but is often done internally to the equipment and isn’t always a direct connection (thus, identify what components you have, get the install guides).
- Equipment grounding bonds all non-current-carrying metal parts to ground. In a PV system, this includes racking, solar panel frames and equipment enclosures.

Hope this helps ...
It does. Thank you.
 
Yes. In a perfect world you'd have 2 fuses, 1 for each 24v bank of batteries but your math is correct.
The old T fuse is a JLLN (littlefuse) and a bit pricey at 250a. Do you by chance know if they are interchangeable with other brands?
 
Any name-brand class-T 300V (not 600V) fuse should be similar.

I'm seeing > $100 from some sources, more in the $40 to $60 range elsewhere.
Blue Sea rebrands one of the top names, probably Littlefuse.





 
Any name-brand class-T 300V (not 600V) fuse should be similar.

I'm seeing > $100 from some sources, more in the $40 to $60 range elsewhere.
Blue Sea rebrands one of the top names, probably Littlefuse.