Depending on distance, maybe one 60A run (6 awg?) from shed to one cabin, daisy chain to second cabin.
Each cabin could have a 30A backfed breaker (one might trip its 30A "main" breaker without affecting the other), or each could have 60A breaker. How many 15A breakers in each cabin? One or the other could use up to all available current this way.
Except, even with 30A breaker, not likely inverter can trip it. Magnetic fast trip (15 milliseconds) requires 5x rated current, 150A or more, which may exceed inverter's surge capability. Below that, takes longer to heat up, likely exceeds 6500W longer than inverter can supply. So larger breakers are just a shut-off,
Depending on distance, maybe one 60A run (6 awg?) from shed to one cabin, daisy chain to second cabin.
Each cabin could have a 30A backfed breaker (one might trip its 30A "main" breaker without affecting the other), or each could have 60A breaker. How many 15A breakers in each cabin? One or the other could use up to all available current this way.
Except, even with 30A breaker, not likely inverter can trip it. Magnetic fast trip (15 milliseconds) requires 5x rated current, 150A or more, which may exceed inverter's surge capability. Below that, takes longer to heat up, likely exceeds 6500W longer than inverter can supply. So larger breakers are just a shut-off, not OCP.
each cabin has 2 -15a breakers . I current bought a main panel that has a 100a breaker so I will just keep that. Below that I will put 2- 30a breakers and run each 30a to the cabin.