I too have decided to use Will Prowse’s “Off Grid King” system. The reason for using 24V to the others is that we are limited on money. We have a 36’ 5th wheel that was mobile but is stationary now so weight and size isn’t an issue any longer. I’d like a 48V system but not switching now. At the time we decided that the 24V met all our needs and we can even add on later. We want this system to supply energy for our a/c 6.5A fridge, 12V water pump and 12V lights. Later we can add more panels and batteries to hopefully run an A/C window unit(s). We don’t need microwave, small appliances or tools. So, here’s what we have. I loaded pictures of my layout but just so you know, I haven’t cut most of the wires yet. I have 6awg for the charge controllers to breakers and then bus bars, also 6awg going to the panels. 2awg to most everything else except the ground wire(12awg), 12V-24V converter is 12awg, and from the battery monitor shunt (18awg) to positive bus bar at battery. When I ordered the bus bars I didn’t know that they were rated so what I have is 250amps. Do I need another size or are these ok? If I’m making any mistakes would you please offer advice for me to correct them. Also, do I need a battery disconnect? I have circuit breakers (50A) from the charge controllers and then more to my panels, but is this correct? Let me know if I’ve missed anything and I’ll post it ASAP. THANKS in advance
 

Attachments

  • image.jpg
    image.jpg
    872.8 KB · Views: 9
  • image.jpg
    image.jpg
    713 KB · Views: 9
  • image.jpg
    image.jpg
    659 KB · Views: 10
  • image.jpg
    image.jpg
    927.9 KB · Views: 10
You need to post info about how you are wiring your panels, panel Voc, and your SCC max input voltage.
50A breakers from panels to SCC will be a nice cutoff switch but your panel amps (4S? 2S2P? 4P?) will never trip these.
 
You need to post info about how you are wiring your panels, panel Voc, and your SCC max input voltage.
50A breakers from panels to SCC will be a nice cutoff switch but your panel amps (4S? 2S2P? 4P?) will never trip these.
4 panels connected in series and then to the 50A breaker and then to the charge controller. 4 more panels to the second charge controller.
 

Attachments

  • image.jpg
    image.jpg
    577.7 KB · Views: 7
  • image.jpg
    image.jpg
    488.3 KB · Views: 5
  • IMG_4452.jpeg
    IMG_4452.jpeg
    1.5 MB · Views: 5
  • IMG_4535.jpeg
    IMG_4535.jpeg
    513.6 KB · Views: 4
  • IMG_4536.jpeg
    IMG_4536.jpeg
    724.2 KB · Views: 7
  • IMG_4534.jpeg
    IMG_4534.jpeg
    536 KB · Views: 5
You need to post info about how you are wiring your panels, panel Voc, and your SCC max input voltage.
50A breakers from panels to SCC will be a nice cutoff switch but your panel amps (4S? 2S2P? 4P?) will never trip these.
I’m horrible at the math for this. I’m not bad at math, I just don’t understand what needs to be inserted into the equation to get the correct answer. I know that series increases the volts and parallel increases the amps but how to figure out anything beyond that, I’m not sure how or even what I’m needing to know. It’s very frustrating for me.
I’ll take a pic of the info on the side of the charge controller (I have to uninstall it) in the morning at sun up.
 
Last edited:
Take a pic of the label on your panels.
Look up the max input voltage of your SCCs.

In series, you add the Voc panel volts (4 times for 4 in series). This plus some voltage increase from temp drop (~15%) absolutely NEEDS to stay below SCC max input voltage.
 
I have two of these EPEVER charge controllers. 40A with four 100 watt panels to each one.
 

Attachments

  • IMG_4542.jpeg
    IMG_4542.jpeg
    703.4 KB · Views: 4
I a
Max input voltage is 150V so you're just fine with 4x 100W panels in series.
How many panels can I add to this? Hopefully have more to add in a month, maybe two.
l also have a pikasola (Amazon) wind turbine generator, 400W, 12v or 24v, 3-phase AC Permanent Magnet Generator, 5 nylon blades. Just the mounting for that thing is going to be a chore and a half. We have a lot of wind here so I figured why not give it a try. Controller system: Electromagnetic/yaw. Any idea where I can go to get assistance with the right and wrongs of this puppy? It’s gonna be awhile before we get to this, like probably next spring, but I figure I should get started studying the process to be prepared. It comes with an anemometer and controller, so I have to figure out the mounting system.
Thanks for all your assistance. It’s reassuring that I didn’t mess up too bad.
 