I am having a serious issue with my two growatts. I started having overheating on a transformer 2 months ago and replaced with the Growatt ATS 5000 auto transformer (×2). When in AC bypass they will show 0 watts and over 6k volts! If I'm in sbu I'm fine. If the batteries have to charge on ac,I'm fine. If I run sub it overheats the transformers (both) and the system either has to be shut down manually or I can switch back to battery and it clears the overload and the transformer will cool back down. Anyone know what could cause this??1000002414.jpg
 
Check to make sure that 60 hz is correctly set.
If it's set to 50 hz that could be the problem.
When connected with the grid, it will match the grid.
When running on battery, it will follow the settings.
 
That is what the inverters are reporting. It's causing massive overheating issues.
Something is seriously wrong.
Have you checked everything with your own meter?
But be extremely careful. Not many meters can handle that voltage. It will explode in your hands.
 
Something is seriously wrong.
Have you checked everything with your own meter?
But be extremely careful. Not many meters can handle that voltage. It will explode in your hands.
I have and it went into shutdown as there were too many volts. It got to 600v and shutdown. I'm thinking of disconnecting the transformers and just run the neutral bond instead to see if the transformers are causing the overloads. I have two 5kw transformers wired in now. It goes ac to inverters. Inverters to transformers and then to a distribution box then to load center.
 
It's hard to believe that they could be that damaged and still turn on.
Really need to see how everything is wired together.
It sounds like a wiring issue.
 
Mat have finally found the issue. When I did the upgrade of the transformers, I bought a new sub panel to use as a distribution panel. I did not know that the panel had a slight bend in the middle behind the busbar. When a heavy load would come on the panel would flex causing one or both breakers to break contact with the busbar. I corrected the issue yesterday and as of right now I am having no issues. I am going to be moving the whole system to a 10x10 building and replacing the growatt inverters with the new eg4 6000xp. When I do I'll replace the faulty panel with a QO panel and installing every piece of safety equipment I can get my hands on.
 