Phocos - Voltronic switches off loads when changing mode

xristostsilis

New Member
Joined
Mar 24, 2022
Messages
109
Hi!

I live in Greece and I have a phocos 5kw 230v inverter. I have it with some diy lifepo4 battery plus a jk BMS without communication from BMS to inverter. I have some voltages set to switch the phocos/voltronic from off grid to grid mode, but I’ve seen that when it switches from off grid to grid mode it turns off the loads for 3 seconds which is very annoying. Any help?
 
Hi!

I live in Greece and I have a phocos 5kw 230v inverter. I have it with some diy lifepo4 battery plus a jk BMS without communication from BMS to inverter. I have some voltages set to switch the phocos/voltronic from off grid to grid mode, but I’ve seen that when it switches from off grid to grid mode it turns off the loads for 3 seconds which is very annoying. Any help?

Some units have two modes - UPS and Appliance. Is it set to UPS?
 
I would assume UPS mode would result in the fastest switchover time.
Hm so it’s not that. I sent an email to phocos but I don’t know when they will answer to me. It’s kinda important so if anyone knows and would like to help would be appreciated
 
so the fw i have already is 3013 for the main and 619 for the display while the latest one available is Main Body (U1) 30.17 and Display Unit (U2) 6.27 (source). I cannot see the release notes for the older fw's that where released in between of the one i have and the latest. Don't know if it's a software bug

inverter model: Any-Grid PSW-H-5KW-230/48V

My current settings are: