120v All-in-one 40A

THUDGUN

New Member
Joined
Jun 6, 2022
Messages
43
So, my Inverter/Charge controller is 120v, but the input is up to 40A. This is from Utility. Does this mean you can run two 120v inputs, on 20A breakers, provided they are on the same phase?
 
You would be better off with a single, larger, breaker. You might have to order one or go to an electrical supply house.
 
So, my Inverter/Charge controller is 120v, but the input is up to 40A. This is from Utility. Does this mean you can run two 120v inputs, on 20A breakers, provided they are on the same phase?
40A@120VAC makes me think that you have a circuit from a load center with a 40 amp breaker connected to the ac_in of your inverter/charger, confirm?
If yes, then typically you would put a load center downstream of your inverter/charger for load distribution.
What is the continous rating in watts for your inverter charger?
 
Yea. That's the form factor of the breakers for my panel. I wasn't going to wire two channels into my inverter, I was just curious and a tad confused. Slowly learning, Thank you.
Again, please provide a product link for your inverter/charger.
 