D Dyotat100 New Member Joined Oct 13, 2020 Messages 214 Jan 11, 2021 #1 I'm going to be using chargery BMS for my 2p4s 12v setup. But I want to use a smart shunt so I can use my phone to check on it. Do I have to use 2 shunts?
I'm going to be using chargery BMS for my 2p4s 12v setup. But I want to use a smart shunt so I can use my phone to check on it. Do I have to use 2 shunts?
snoobler Solar Honey Badger Joined Jul 10, 2020 Messages 8,387 Location HBR, AZ Jan 11, 2021 #2 Why do you wonder if you need two shunts?
D Dyotat100 New Member Joined Oct 13, 2020 Messages 214 Jan 11, 2021 #3 Never mind. I called Thornwave Labs. They have a Bluetooth setup that will use a existing shunt. I wasn't sure if I had to use a smart shunt and the chargery shunt so both could do there thing
Never mind. I called Thornwave Labs. They have a Bluetooth setup that will use a existing shunt. I wasn't sure if I had to use a smart shunt and the chargery shunt so both could do there thing
Bob B Emperor Of Solar Joined Sep 21, 2019 Messages 8,739 Jan 11, 2021 #4 As long as the shunt is 75mv or less you can use the Chargery with it instead of having 2 ...... You would have to calibrate the chargery.
As long as the shunt is 75mv or less you can use the Chargery with it instead of having 2 ...... You would have to calibrate the chargery.
D Dyotat100 New Member Joined Oct 13, 2020 Messages 214 Jan 11, 2021 #5 I found out I can use the chargery's shunt. Thanks