Is anyone running 3 EG4 6500s in 240 split phase with 2 units running 2P1 and one unit running 2P2 180? Seems like it should work, maybe a good way to run a system that has an unbalanced load.
I ran my system like that for about 4 months before I got my 4th eg4. I had to put more of the 120 loads on the leg with the two inverters. Ran fine like that