Have a rack of 6 eg4 48v batteries. Any recommendations on a 48v charger for those sunless days
Yep, especially in the 48V sector - even less common than 12/24V systems seen in automotive & heavy equipment.. and the reason why I went with a hybrid inverter. I didn't have to worry about 3 (or more) separate components to handle what the hybrid inverter can.IMHO the inverter/charger pretty much ate the breakfast of the discrete ac2dc charger.
This is an excellent inverter/charger which includes an excellent charger.
Samlex EVO-4248SP 4200W, 48V Split Phase Pure Sine Inverter/Charger | DonRowe.com
The Samlex America EVO-4248SP, 4200 Watt, 48 VDC, 120/240 VAC Split Phase Pure Sine Wave Inverter/Charger with 60 Amp Charger is a rugged inverter/charger designed for back up and off-grid applicationswww.donrowe.com
Sorry, we are off grid. And I have a generator but need a charger to run it to the battery bank. Or maybe I don’t. I’m newThe grid? A generator?
What sort of inverter do you currently have?Sorry, we are off grid. And I have a generator but need a charger to run it to the battery bank. Or maybe I don’t. I’m new
You can use your generator as the AC input source to the inverter and charge your batteries that way. I'll see what the lead time is on the 48V charger and let you know. But if you have a rack of 6 batteries, charging through the inverter will be the most efficient course of action.eg4 6500 ex48v
Ok, so basically just and extension cord to the ac input of one of the charge controllers? Will it be an issue to only hook 1 of the 2 inverters to the generatorYou can use your generator as the AC input source to the inverter and charge your batteries that way. I'll see what the lead time is on the 48V charger and let you know. But if you have a rack of 6 batteries, charging through the inverter will be the most efficient course of action.
Ok, thank you very muchI don't see why there would be any effect by only using one unit other than it limits your max amps possible. Probably irrelevant based on the generator limitation.
Could you explain how that would look?An extension cord is not going to be best practice. The generator should run into the AC input of the master inverter after running through subpanel.
How many other people have inverter chargers but think they have inverters only?eg4 6500 ex48v
When using the grid and/or a generator with multiple inverters, we recommend a subpanel or something that will allow you to overcurrent protect each individual line with breakers. Powering that subpanel with the generator and having breakered connections to each inverter in the system (making sure that all of the Line 1 inverters are on the grid/gen's Line 1, and vice versa) will evenly split the power draws to each line as they have demand for it. Pulling generators over their 50-60% mark can cause the generated sine wave to distorted past 3% harmonic distortion which will damage inverters over time, so you want to make sure that will not happen. It's always advised to have the consultation or supervision of a licensed professional when installing electrical connections.Could you explain how that would look?