Jankzilla
New Member
- Joined
- Oct 7, 2022
- Messages
- 6
Hi guys,
I have a question about AC breaker size. My impression was that the breaker needs to be spec'd for the max sustained output of the inverter. So in my case I have a Goodwe GW3048-EM which has a max ouput (while grid supplied) of 3kW. So if I add 25% I get 3.75kW, divided by 230V is 16.3A. Supposedly you can round down if you are less than half an amp over the nearest standard size. So presumably 16A breakers would be fine.
However I am a bit perplexed by something on the data sheet. It says "Max. Apparent Power from Utility Grid - 5300VA". Now I know there is a bunch of stuff related to power factor and the types of loads you run (though you shouldn't be running heavy inductive loads on this inverter at all) resulting in a difference in your real power vs apparent power. But I just don't know where that number comes from. My thought was that it could be a momentary number for a few milliseconds, or perhaps if you are passing 3kW through from the grid and charging the batteries at 2.4kW? My assumption is that is not possible with this inverter, though I could be wrong.
At any rate, if anyone could help explain this or point me in the right direction I would appreciate it. I'm pretty sure 16A would work but I'm trying to make sure I understand what I am doing, not just making something that should probably work.
JZ
I have a question about AC breaker size. My impression was that the breaker needs to be spec'd for the max sustained output of the inverter. So in my case I have a Goodwe GW3048-EM which has a max ouput (while grid supplied) of 3kW. So if I add 25% I get 3.75kW, divided by 230V is 16.3A. Supposedly you can round down if you are less than half an amp over the nearest standard size. So presumably 16A breakers would be fine.
However I am a bit perplexed by something on the data sheet. It says "Max. Apparent Power from Utility Grid - 5300VA". Now I know there is a bunch of stuff related to power factor and the types of loads you run (though you shouldn't be running heavy inductive loads on this inverter at all) resulting in a difference in your real power vs apparent power. But I just don't know where that number comes from. My thought was that it could be a momentary number for a few milliseconds, or perhaps if you are passing 3kW through from the grid and charging the batteries at 2.4kW? My assumption is that is not possible with this inverter, though I could be wrong.
At any rate, if anyone could help explain this or point me in the right direction I would appreciate it. I'm pretty sure 16A would work but I'm trying to make sure I understand what I am doing, not just making something that should probably work.
JZ