Hi, i have 2 more or less compatible same type, same power, same Firmware Deye 5Kw Hybrid.
My current problem is the BMS... or better the "No communicating BMS" and low Grid Voltage (Philippines).
The Inverters run until today in tandem/parallel like in the manual.
But because of the non communicating BMS both inverters have different meanings about the SoC (2 bridged No Name 150Ah 48V 15S with S.M.A.R.T BMS), after reaching +/- 80% SoC, Master Inverter 1 is still trying to charge the Batteries, and the Slave Inverter 2 stops production of Solar Energy and starts to discharge the batteries.
E.g. at 12 Noon Inverter 1 ist charging by Solar with 2.5Kw, 2nd Inverter is not using Solar, instead he uses Battery power for Output.
The both Panel sets are side by side and have the same Sun & the same power the whole Day.
I did not get the BMS to communicate via RS232 with the Inverter (maybe just a wiring problem, but i don't have PIN Layout for the BMS RS485), so i ordered 2 new BMS with CAN to replace the existing BMS and to make everything smooth... i hope.
In the meanwhile i want to run the inverters on AC Coupling in UPS Mode with 10Kw AC Peak. Possible?
Why UPS? We have Grid Voltage down to 195 Volt and i want to power the House appliances with 230 Volt 60Hz.
Why Coupling? We have sometimes Demand for 6-7 Kw Peak for two welding machines.
Config:
Every Inverter has one 150Ah/48V/7.5Kw Battery, every Inverter has 8 Panel/4Kw Peak Solar. Grid is single phase 60Hz 230 Volt (More exact: 230V Line to line, little bit like Split phase, but no Zero-potential, so more Single Phase than Split phase "Davao Light")
1st Inverter is attached to the grid, House load is attached to the LOAD Exit, CT is clamped to the Grid Supply cable.
2nd Inverter is attached with his GRID to the LOAD of the first Inverter, CT is clamped to this connection.
My Wish is to have booth inverters giving the same Power to the House, e.G. House demands for 3Kw, Inverter 1 is delivering 1.5Kw to the House LOAD, and Inverter 2 is also delivering 1.5 Kw to the House.
Is this possible? Do in need to change the wiring or the parameters?
I know i can put the 2nd inverter to the GEN Input of the first Inverter, but in this case the output is limited to 5 KW, i am right?
We have sometimes 2 Welding Inverters, Power need goes up to 6 or 7 Kw peak. That's the reason i want to parallel the inverters to have 10 Kw Peak.
It would also be ok to set the 2nd Inverter to put up to e.g. 500 Watts to the "local Grid" or "Micro Grid", and only rise on Load.
My current problem is the BMS... or better the "No communicating BMS" and low Grid Voltage (Philippines).
The Inverters run until today in tandem/parallel like in the manual.
But because of the non communicating BMS both inverters have different meanings about the SoC (2 bridged No Name 150Ah 48V 15S with S.M.A.R.T BMS), after reaching +/- 80% SoC, Master Inverter 1 is still trying to charge the Batteries, and the Slave Inverter 2 stops production of Solar Energy and starts to discharge the batteries.
E.g. at 12 Noon Inverter 1 ist charging by Solar with 2.5Kw, 2nd Inverter is not using Solar, instead he uses Battery power for Output.
The both Panel sets are side by side and have the same Sun & the same power the whole Day.
I did not get the BMS to communicate via RS232 with the Inverter (maybe just a wiring problem, but i don't have PIN Layout for the BMS RS485), so i ordered 2 new BMS with CAN to replace the existing BMS and to make everything smooth... i hope.
In the meanwhile i want to run the inverters on AC Coupling in UPS Mode with 10Kw AC Peak. Possible?
Why UPS? We have Grid Voltage down to 195 Volt and i want to power the House appliances with 230 Volt 60Hz.
Why Coupling? We have sometimes Demand for 6-7 Kw Peak for two welding machines.
Config:
Every Inverter has one 150Ah/48V/7.5Kw Battery, every Inverter has 8 Panel/4Kw Peak Solar. Grid is single phase 60Hz 230 Volt (More exact: 230V Line to line, little bit like Split phase, but no Zero-potential, so more Single Phase than Split phase "Davao Light")
1st Inverter is attached to the grid, House load is attached to the LOAD Exit, CT is clamped to the Grid Supply cable.
2nd Inverter is attached with his GRID to the LOAD of the first Inverter, CT is clamped to this connection.
My Wish is to have booth inverters giving the same Power to the House, e.G. House demands for 3Kw, Inverter 1 is delivering 1.5Kw to the House LOAD, and Inverter 2 is also delivering 1.5 Kw to the House.
Is this possible? Do in need to change the wiring or the parameters?
I know i can put the 2nd inverter to the GEN Input of the first Inverter, but in this case the output is limited to 5 KW, i am right?
We have sometimes 2 Welding Inverters, Power need goes up to 6 or 7 Kw peak. That's the reason i want to parallel the inverters to have 10 Kw Peak.
It would also be ok to set the 2nd Inverter to put up to e.g. 500 Watts to the "local Grid" or "Micro Grid", and only rise on Load.