cschill2020
New Member
Hi,
I am located in San Jose, CA. I am working on building a battery backup system. I have 44kWh 48V LifePO4 batteries with Seplos BMS.
I have a 100A subpanel handling critical loads that is currently utility powered. Max power from that panel is ~3kW @ 120V ~= 30A. No 240 yet... In phase 1, I would like to connect the batteries as a backup source to the subpanel using a hybrid inverter.
Now the next piece of the puzzle is where I would like some feedback. Which inverter/charger would you recommend for this setup? I am currently considering starting with a Victron Multiplus-II 5kW and potentially adding a 2nd if I need 240V (e.g. adding an EV charger).
Phase 2 is adding solar to charge the batteries. I can easily support 25 400W panels, but I would probably start with ~6500kW, 16 panels (4S4P). So I want to add a Victron MPPT 250 controller on top of this. Any other considerations I should have for such a system?
I talked to a rep at a local solar equipment company and they mentioned that I may run into issues with the utility (PG&E) for such a system. The rep suggested looking at a grid-tied inverter like Tigo. I guess one of the issues with Victron is lack of UL certs. In any case, I am not planning on feeding the utility given current NEM3 rates. Victron and Seplos are compatible. I am not sure about Seplos and Tigo compatibility...
Finally, I am not sure what all I should be considering with respect to distribution and fusing. I am looking for resources on what additional components I should consider on top of the inverter and MPPT.
Thank you!
I am located in San Jose, CA. I am working on building a battery backup system. I have 44kWh 48V LifePO4 batteries with Seplos BMS.
I have a 100A subpanel handling critical loads that is currently utility powered. Max power from that panel is ~3kW @ 120V ~= 30A. No 240 yet... In phase 1, I would like to connect the batteries as a backup source to the subpanel using a hybrid inverter.
Now the next piece of the puzzle is where I would like some feedback. Which inverter/charger would you recommend for this setup? I am currently considering starting with a Victron Multiplus-II 5kW and potentially adding a 2nd if I need 240V (e.g. adding an EV charger).
Phase 2 is adding solar to charge the batteries. I can easily support 25 400W panels, but I would probably start with ~6500kW, 16 panels (4S4P). So I want to add a Victron MPPT 250 controller on top of this. Any other considerations I should have for such a system?
I talked to a rep at a local solar equipment company and they mentioned that I may run into issues with the utility (PG&E) for such a system. The rep suggested looking at a grid-tied inverter like Tigo. I guess one of the issues with Victron is lack of UL certs. In any case, I am not planning on feeding the utility given current NEM3 rates. Victron and Seplos are compatible. I am not sure about Seplos and Tigo compatibility...
Finally, I am not sure what all I should be considering with respect to distribution and fusing. I am looking for resources on what additional components I should consider on top of the inverter and MPPT.
Thank you!