SCE (Edison) sent a few people out last week to confirm that I could upgrade to 200A service. I talked to them, asked questions, and they confirmed on the spot (and follow-up phone call) that I was okay to install and 200A service panel. I already have an active permit. However, I remember the electrician saying I had 1/0 service wiring to the house, so I'm good to go. I didn't research it at the time, and I have now, and I've read that I'd need minimum 2/0 copper to put in a 200A breaker. Either I heard him wrong or I got bad info. I'm going to follow up with them again after the weekend to have them clarify. I currently have 100A service panel.
Regardless of that, if I do have 1/0 wiring to the house, I should still be capable of 150A from what I've read. I plan to to still upgrade to a 200A panel (225 bus) and put in a 150A main breaker if the original wiring info of 1/0 I got was correct.
My plan is for an 8kW system, grid-tied, Sol Ark 15K inverter, 20x 400W Q Cell panels, and 30kWh (6x LifeForce4 100 AH batteries with hub) battery backup.
Would I be making the right move in going with a 200A panel with 150A breaker to give myself enough (120% rule) backfeed potential? Maybe it's not necessary with an 8kW system? Should I be looking at the Sol Ark 12K or maybe the EG4 18K instead of the Sol Ark 15K?
Just looking to verify some things before I have my plans drawn up and submit to the city and Edison. And definitely before I buy anything.
Thanks.
Regardless of that, if I do have 1/0 wiring to the house, I should still be capable of 150A from what I've read. I plan to to still upgrade to a 200A panel (225 bus) and put in a 150A main breaker if the original wiring info of 1/0 I got was correct.
My plan is for an 8kW system, grid-tied, Sol Ark 15K inverter, 20x 400W Q Cell panels, and 30kWh (6x LifeForce4 100 AH batteries with hub) battery backup.
Would I be making the right move in going with a 200A panel with 150A breaker to give myself enough (120% rule) backfeed potential? Maybe it's not necessary with an 8kW system? Should I be looking at the Sol Ark 12K or maybe the EG4 18K instead of the Sol Ark 15K?
Just looking to verify some things before I have my plans drawn up and submit to the city and Edison. And definitely before I buy anything.
Thanks.