Looking at breaker change for 120% rule. With 200a feed, what determines a panel's amps - manufacture label, main breaker, volume for larger wires? Is code OK with changing a 200a panel's 200a main to 225a main breaker, or do I need a 225a panel? I assume you can change a 200a panel to a 175a, or lower, main breaker without code issues other than total breaker amps.
Currently have a 100a line to a 100a shop panel that I want to replace - old, ugly, and no breaker slots left. Trenching a new URD 200a line to a new 225a panel that takes inverter's grid tied AC out. Replace the 100a panel with a 150a panel, use old 100a main breaker, and save the 150a panel's 150 main for the new 225a panel.
The existing 100a panel works but I could tap the new 225a to the 100a replacement panel. That would surplus 300+ ft of 4awg cable (1987 code?) and its 1.5in buried conduit. Conduit is too small for 200a cable and 4awg probably too large for for panel connections. Run a string line in case a hybrid shows up some day and I need distant CTs.
Would a 4awg ALU serve as ground for a 200a feed, some charts show 2awg? One less URD wire to run. Shop panel was first on site and has its own ground with a copper wire going into the ground under the slab. New buildings added new panels and the shop 100amps changed from grid to a new panel, but ground was never moved. So the home has its ground and the shop its own ground and that needs to change.
Currently have a 100a line to a 100a shop panel that I want to replace - old, ugly, and no breaker slots left. Trenching a new URD 200a line to a new 225a panel that takes inverter's grid tied AC out. Replace the 100a panel with a 150a panel, use old 100a main breaker, and save the 150a panel's 150 main for the new 225a panel.
The existing 100a panel works but I could tap the new 225a to the 100a replacement panel. That would surplus 300+ ft of 4awg cable (1987 code?) and its 1.5in buried conduit. Conduit is too small for 200a cable and 4awg probably too large for for panel connections. Run a string line in case a hybrid shows up some day and I need distant CTs.
Would a 4awg ALU serve as ground for a 200a feed, some charts show 2awg? One less URD wire to run. Shop panel was first on site and has its own ground with a copper wire going into the ground under the slab. New buildings added new panels and the shop 100amps changed from grid to a new panel, but ground was never moved. So the home has its ground and the shop its own ground and that needs to change.