Any issue running both MPPTs to the same post on Lynx?

corn18

Village Idiot
Joined
Sep 9, 2021
Messages
816
Need to free up a spot on my Lynx. Currently have 2 100/50 MPPTs going to individual posts on the Lynx each using 6 ga wire and a 60A mega fuse. Was going to double them up and use a 125A fuse. Each 6 ga will only carry a max of 50A (max output of the 100/50 MPPT). The outgoing wire to the batts is 2x4/0. Am I missing anything?
 
You can add a fuse or two to the end of a Lynx. The problem with doing it your way is you really need a fuse that's rated at 1 of the cables not both combined. If one pulls 100a and other 0 it won't blow the 125a fuse.

 
6 ga wire is rated for 120A in free air. 125A fuse would protect the wire effectively, wouldn't it?
 
6 ga wire is rated for 120A in free air. 125A fuse would protect the wire effectively, wouldn't it?
It's not free air there's jacket on the copper wire, what's the temp rating of the jacket and what's that max amperage? If issue your wire will melt the jacket and still flow power until it touches metal and shorts or sets fire.

I think I have 2 mppts wired into 1 port on my Lynx but it's 4ga using 100a fuse and the mppts are 150/100 huge ones with under 2kw solar on each at 48v so 40a is running through them.
 
It's not free air there's jacket on the copper wire, what's the temp rating of the jacket and what's that max amperage? If issue your wire will melt the jacket and still flow power until it touches metal and shorts or sets fire.

I think I have 2 mppts wired into 1 port on my Lynx but it's 4ga using 100a fuse and the mppts are 150/100 huge ones with under 2kw solar on each at 48v so 40a is running through them.
I thought free air in the Blue Sea calculator meant it isn't in an engine room or conduit.

Temp rating is 105 deg C max amps is 115A. I get all my cables from Windy Nation.
 
Last edited:
I thought free air in the Blue Sea calculator meant it isn't in an engine room or conduit.
Idk don't think so. I assumed it meant free air like copper in free air, such as ground wiring and such where it's fully exposed
 
Idk don't think so. I assumed it meant free air like copper in free air, such as ground wiring and such where it's fully exposed
Seems NEC does not make it very clear, either.

 
Seems NEC does not make it very clear, either.

Yeah it doesn't say insulated conductor or anything about the jacketing. Power lines are open air conductors as are heat exchangers and other wiring inside a device.

I'm sure there's a calculator that'll show you how hot 100amps through 6gauge copper wire gets
 