B b.shaw New Member Joined Dec 9, 2022 Messages 11 Mar 11, 2024 #1 With 20' between the Sol-Arks and the batteries, would I be better off with individual cables to the batteries (A) or a heavier gage wire between and a junction box near the Sol-Arks (B)?
With 20' between the Sol-Arks and the batteries, would I be better off with individual cables to the batteries (A) or a heavier gage wire between and a junction box near the Sol-Arks (B)?
sunshine_eggo Happy Breffast! Joined Oct 26, 2021 Messages 16,120 Location HBR, USA (6500' in ENE AZ) Mar 11, 2024 #2 It really comes down to cost. Since I don't know what Sol-ark, I used 5kW for each inverter. For A: Voltage Drop Calculator This free voltage drop calculator estimates the voltage drop of an electrical circuit based on the wire size, distance, and anticipated load current. www.calculator.net 2awg x2 for 20' @ 200A/51.2 = 1.22% losses For B: Voltage Drop Calculator This free voltage drop calculator estimates the voltage drop of an electrical circuit based on the wire size, distance, and anticipated load current. www.calculator.net 2/0 for 20' @ 200A/51.2V = 1.22% losses.
It really comes down to cost. Since I don't know what Sol-ark, I used 5kW for each inverter. For A: Voltage Drop Calculator This free voltage drop calculator estimates the voltage drop of an electrical circuit based on the wire size, distance, and anticipated load current. www.calculator.net 2awg x2 for 20' @ 200A/51.2 = 1.22% losses For B: Voltage Drop Calculator This free voltage drop calculator estimates the voltage drop of an electrical circuit based on the wire size, distance, and anticipated load current. www.calculator.net 2/0 for 20' @ 200A/51.2V = 1.22% losses.