I'm hoping to set up a simple battery charger for my LifePO4 batteries. I'm charging 1 battery at a time. I have both 12v and 24v 100AH. I have a Victron 75 15 (12/24v) charger and 2 BougeRV N-Type 200w solar panels. The solar panels are 36.4v VOC and 6.3imp (amps). I know I can't wire the two panels in series because that would be 72.8 volts which is too close to the Victron's limit of 75. The Victron manuals says the nominal wattage is 220w at 12v and 440w at 24v.
So, if I wire the panels in parallel (400w), I can charge the 24v batteries but have to unplug one solar panel when charging 12v batteries because of the nominal wattage limit on the Victron charge controller? All the videos I've watched say you have to watch the voltage but can have excess amperage . . . apparently not because of the Victron's wattage limit.
I'm guessing I need a more capable solar controller but need to understand this so I don't buy another throw away.
Thank you!
So, if I wire the panels in parallel (400w), I can charge the 24v batteries but have to unplug one solar panel when charging 12v batteries because of the nominal wattage limit on the Victron charge controller? All the videos I've watched say you have to watch the voltage but can have excess amperage . . . apparently not because of the Victron's wattage limit.
I'm guessing I need a more capable solar controller but need to understand this so I don't buy another throw away.