Also I have a detailed write-up that I just lost of what I tested today. Basically, I received a replacement inverter from you guys yesterday delivered evening... Almost 1000usd just to get the refurbed one here. The thing looks like it been through a way. Hole in the side. Top screws stripped. But who cares as long as it works. Also there was no certificate of why this inverter was returned or report stating it was tested before shipment.. I thought that would have been almost required but...anyways.
I opened it. Warranty is out the window anyway. There is also no screw based on the location you quoted. No problem.
I attempted to set up as off grid just to test. No grid input on any of those terminals. From my understanding the program 34 set to ENA means it enables the bypass relay and allows NG bond from a main panel to pass through IF grid is detected. If grid is not detected the relay should create its own and bond at the inverter even without a bond screw.
Now my tests for this seem inconclusive. I have the new inverter bench setup just batteries and output terminals. 34 to ENA.
H2 to N 133v.
H1 to N 108v
G to N 14v.
H2 or H1 to N 120v.
Does this indicate the bond in the inverter is not present as I have current on my Ground?
Also did a subsequent test to detect what change would be if Program 34 Disabled. No change...
H2 to N 140v.
H1 to N 106v
G to N 420v.
H2 or H1 to N 120v
Now onto the next issue which my original inverter was having the same issue with. This refurb one does the exact same thing. Barely 18 cycles on the batteries in total since August last year!
I set up the grid input as neither of the inverters handle the bond correctly it seems.(I am subject to correction on this based on my previous test)
With 34 Enabled, grid input(bonded main panel) H1, H2, N and G into the input terminals of the inverter. I finally get the pass through bond and proper voltages on inverter output terminals.
H1 to N 120v
H2 to N 120v
H1 to G 120v
H2 to G 120v
N to G 0.4 or less volts
But continuity N to G is like 150ohms. Shouldn't it be full continuity like 0.0x resistance value? (Correct me if I'm wrong or 150 ish ohms is acceptable on the output)
Now im not going to run the fridge as that is pretty important. I used a hair dryer 1875w rating, actually pulling 1.56kw. Should be able to easily handle that on one leg.
The hair dryer runs for undetermined amounts of minutes then BP battery disconnect error. SAME error I was getting with previous inverter. I have BMS tools open and monitoring the batteries there was no under volt or over current faults recorded. Just BP on inverter.
BMS tools reported 89/90% at start of the test so it's impossible it can undervolt a battery that was reporting 52ish volts and if it did. It should have occurred at the start. So is it possible this inverte has the same issue?
Two. I tried this on both batteries in parallel. Also individually just to see if one battery was causing the issue. Nothing. I borrowed a growatt inverter 6k and the batteries pull from it fine without issue.
Sorry for the long winded information but. This is crazy. Again. Tell me if I missed anything at all here please.