Hi, I have approx 2K of 3S/3P panels (74V/30A - total) fused at 15A per string at my combiner box with voltage drop of 0.50% on my run.
Then from my 80A/200V CC to the 24V Battery bank's busbar, wired with (4AWG) and fused with a 100A breaker.
Now, I am at the batteries to the 24v inverter.
I will be using (4) 12V 300ah batteries (200A BMS/ea.) in series/parallel for a 24V 600Ah battery bank (with balancers) to a 24V 4K inverter.
Fusing at the batteries (2S2P), do I place an MRBF fuse at each positive terminal on each 24V 300AH battery string - 2P (2 fuses in total) or at every battery's positive terminal (4 in total) and do I use the 200A Max Continuous Discharge Current - BMS for my fuse rating? 200x1.25=250A MRBF Fuse or the batteries 300Ah rating which would max out with a MRBF at 300A?
I'm looking at using 4/0.
Then from my 80A/200V CC to the 24V Battery bank's busbar, wired with (4AWG) and fused with a 100A breaker.
Now, I am at the batteries to the 24v inverter.
I will be using (4) 12V 300ah batteries (200A BMS/ea.) in series/parallel for a 24V 600Ah battery bank (with balancers) to a 24V 4K inverter.
Fusing at the batteries (2S2P), do I place an MRBF fuse at each positive terminal on each 24V 300AH battery string - 2P (2 fuses in total) or at every battery's positive terminal (4 in total) and do I use the 200A Max Continuous Discharge Current - BMS for my fuse rating? 200x1.25=250A MRBF Fuse or the batteries 300Ah rating which would max out with a MRBF at 300A?
I'm looking at using 4/0.