I'm posting here to share some insights I recently gained while helping a client. I had to reach out to AIMS Technical Support, who confirmed that their manual is lacking in detail and could be improved significantly.
Unit installed
Link to manual
I have a client who had another solar installer sell and install an AIMS 10K Inverter/Charger for residential use. Although this device is primarily intended for marine applications, such as on boats, it functions quite well as a standard inverter.
The client wanted the generator start feature to work, but the previous installer was unable to configure it and seemed not to have made a genuine effort.
To add complexity, the client uses six EG4 LifePower4 batteries, which the inverter/charger does not natively support. The closest supported chemistry is Gel, which bulk charges to 56V and floats at 54.8V—slightly high for float which actually won't float on generator input anyway, but acceptable for bulk charging.
According to the manual, the generator is activated when the "low battery alarm" is triggered, but the manual does not specify the voltage for this alarm. After consulting with AIMS, I learned that the "low battery alarm" is set 1V higher than the low battery trip point. With the Gel setting and dip switch 1 in position 1, the low battery alarm triggers at 47V, and the low battery trip point triggers at 46V.
Unfortunately, with this inverter, the LifePower4 batteries must drain to 47V, approximately 5% state of charge (SOC), before the inverter triggers the low battery alarm and starts the generator. The generator then charges the batteries to 56V before shutting off. According to EG4 documentation (page 5) the battery will shut off between 47-44V depending on load, hopefully, it doesn't shut off before the inverter detects and activates the low battery alarm.
While this configuration is not ideal, and certainly nothing I would install, it should function adequately, especially during summer months when the air conditioning runs all night and the battery bank might be completely drained and need the generator to activate and recharge the batteries.
I’m open to other ideas or perspectives on the configuration that don't involve additional equipment purchases, as the client has already spent enough. I'm posting this here to help anyone else who might encounter this situation, in hopes that this information will be indexed by Google or appear in DIY Solar search results for others to benefit from.
Cheers!
Unit installed
Link to manual
I have a client who had another solar installer sell and install an AIMS 10K Inverter/Charger for residential use. Although this device is primarily intended for marine applications, such as on boats, it functions quite well as a standard inverter.
The client wanted the generator start feature to work, but the previous installer was unable to configure it and seemed not to have made a genuine effort.
To add complexity, the client uses six EG4 LifePower4 batteries, which the inverter/charger does not natively support. The closest supported chemistry is Gel, which bulk charges to 56V and floats at 54.8V—slightly high for float which actually won't float on generator input anyway, but acceptable for bulk charging.
According to the manual, the generator is activated when the "low battery alarm" is triggered, but the manual does not specify the voltage for this alarm. After consulting with AIMS, I learned that the "low battery alarm" is set 1V higher than the low battery trip point. With the Gel setting and dip switch 1 in position 1, the low battery alarm triggers at 47V, and the low battery trip point triggers at 46V.
Unfortunately, with this inverter, the LifePower4 batteries must drain to 47V, approximately 5% state of charge (SOC), before the inverter triggers the low battery alarm and starts the generator. The generator then charges the batteries to 56V before shutting off. According to EG4 documentation (page 5) the battery will shut off between 47-44V depending on load, hopefully, it doesn't shut off before the inverter detects and activates the low battery alarm.
While this configuration is not ideal, and certainly nothing I would install, it should function adequately, especially during summer months when the air conditioning runs all night and the battery bank might be completely drained and need the generator to activate and recharge the batteries.
I’m open to other ideas or perspectives on the configuration that don't involve additional equipment purchases, as the client has already spent enough. I'm posting this here to help anyone else who might encounter this situation, in hopes that this information will be indexed by Google or appear in DIY Solar search results for others to benefit from.