Panel frames, mounting rails, metalic conduit and J boxes all are grounded to the Green wire which runs all the way back to the main panel and down to the grounding rod.
Depending on distance, it is possible to install a separate grounding rod near the panel array but is not recommended unless there is no alternative.
But grounding a dc solar line wouldn't pop any breaker in a short to ground and would leave the metallic conduit energized and then feed that voltage to every grounded object via the bond in the panel, no?technically a proper ground isn't "connected" to anything ("ac" side or "dc" side) unless something is failing.
it's linking all of the non connected objects that we touch together so they ideally maintain same balance of static charge. Of course if something fails it also gives a path to hopefully pop a fuse / breaker
This serves no purpose. As you still need the EGC ran back to the existing grounding system for protection.Depending on distance, it is possible to install a separate grounding rod near the panel array but is not recommended unless there is no alternative.
Hi,But grounding a dc solar line wouldn't pop any breaker in a short to ground and would leave the metallic conduit energized and then feed that voltage to every grounded object via the bond in the panel, no?
That would depend on if your equipment includes any DC ground fault detection or protection.But grounding a dc solar line wouldn't pop any breaker in a short to ground and would leave the metallic conduit energized and then feed that voltage to every grounded object via the bond in the panel, no?
I think I worded that wrong, sorry.Hi,
There is a difference between positive/negative wires on the solar panel and ground in this case. The smarter folks could correct me if this is not so.
The grounding discussed here is grounding the panel frames, and anything else metal on the array system.
It won’t. This is for bonding only.But grounding a dc solar line wouldn't pop any breaker in a short to ground and would leave the metallic conduit energized and then feed that voltage to every grounded object via the bond in the panel, no?
Yup, I know.(And this bonding is the way NEC wants you to do it anyway)
Yup, I know.
And it doesnt seem thoughtful or fruitful. If in fact now in a fault, the entire frame is carrying potential with no breaker. What if the other conductor finds a way to a frame? LOTS of arcs and fire.
What you have to understand is that there is no fault unless there is a path for current to flow.Yup, I know.
And it doesnt seem thoughtful or fruitful. If in fact now in a fault, the entire frame is carrying potential with no breaker. What if the other conductor finds a way to a frame? LOTS of arcs and fire.
put a breaker on it thenYup, I know.
And it doesnt seem thoughtful or fruitful. If in fact now in a fault, the entire frame is carrying potential with no breaker. What if the other conductor finds a way to a frame? LOTS of arcs and fire.
How would it trip?put a breaker on it then
YesWhat is the most recommended way to ground all of them? Run a ground from each array back the solar shed and ground them to the AC panel's ground?
Connect to your grounding system, at the closest location to the SCC.If so would it be the AC panel from the grid or AC panel after the inverters or both?
YesShould those two ac panels be grounded together as well?
Yes
Connect to your grounding system, at the closest location to the SCC.
Yes
There should only be one grounding system for everything.
Everywhere you run circuit conductors, an EGC should be ran with them.
All EGC's should be bonded (connected) together at every location. Along with all equipment, enclosures, boxes, raceways, and framing.
Yes, that's how it should be done.Can I run the ground from the arrays in the same conduit as the pv wire that goes to the inverters?