"In the 2020 code RV pedestals are explicitly excluded from the need for 30- and 50-amp GFCI protection for the following reasons:
— The 30- and 50-amp power on the RV pedestal are considered feeder circuits (those circuits that feed another panel) and not branch circuits. The changes made in 2017 applied to branch circuits, such as the 20-amp receptacle on an RV pedestal, not feeder circuits.
— The leakage current allowed by UL for GFCI circuits when all the downstream GFCI receptacles are added together would be enough to constantly trip the pedestal GFCI circuit."
https://www.rvtravel.com/30-and-50-amp-gfcis-in-campgrounds/
"I never said that, and here’s why. I have anecdotal evidence to back up my theory that total ground leakage currents in an RV shore power connection can easily total more than 5 mA. That’s because everything you plug into your RV leaks a little current to ground. That includes your microwave, stove, battery charger, inverters, air conditioner and control systems.
Most of these leakages are allowed by UL and the NEC, but each one could easily be 0.5 mA or so, with switching power supplies for your 12-volt converter having an exception to allow up to 3 mA of leakage (or thereabouts)."
https://wizard-of-watts.com/2020/03/15/the-revised-nec-551-71f-for-rv-parks/
https://www.jadelearning.com/blog/nec-rv-vehicles-and-parks-gfci-protection/
2020 NEC – Tentative Interim Agreement RV Vehicles & Parks, Section 551.71(F), GFCI Protection
The intent of this TIA is to clear up a potential conflict in the Code. Although the TIA has not been processed through the entire standards development process, it is enforceable code language. It is interim since it is effective only between editions of the Code. It is automatically considered for the next code cycle and will be subjected to all of the procedures of the standards development process. This is a good example of why it is important for both installers and inspectors to keep up with code changes that occur between cycles.
In Summary: ...The cumulative leakage could exceed the trip threshold of a Class A GFCI protection, resulting in nuisance tripping.
A customary practice for curing this is clipping off the ground pin on the RV feeder cord, which could have disastrous results.