Would it be easier if we designed it so the single phase from the grid was only used to charge the batteries, and not power the loads? possibly separate battery banks with separate chargers, and the grid charging one at a time. Excuse me if I'm totally off base here.
thank you
PV/battery systems do fail, so it is good to have grid as backup to power loads directly. If you have 3-phase loads and 3-phase grid, you can do that with a transfer switch. I'm setting up 3-phase inverter for 3-phase shop tools, but will continue to have single phase service because price to get 3-phase was too high (even though available as high voltage on a pole only 200' away.)
I would have installed 3-phase HVAC, but will probably use single-phase so my inverters aren't needed to heat the house. VFD can also power 3-phase motors more cheaply and reliably than an inverter/battery system.
3-phase loads of course start better and have more torque. Battery inverter has to be able to deliver starting surge.
Good battery chargers are expensive (those that carefully regulate battery voltage, but inverter/chargers are common. You can charge battery with either single phase or three phase. If charging with 3-phase and powering 3-phase loads, ripple on battery should be eliminated because power delivery is constant. If powering single phase from battery, there is ripple on the battery (of full current, capacitors can't smooth that), and if charging at same time, single phase grid will not be in sync, so ripple still present. Not terrible, that is normal for battery/PV system, but if inverters can pass through the single or 3-phase grid to load, battery can be kept at float, probably last longer.
My systems are SMA Sunny Island, which pass through grid (or generator), and can add power from battery synchronized to grid (in the event current draw is higher than what input can deliver). They also have Sunny Boy or Sunny TriPower, which use PV and also deliver synchronized AC power.
48V battery
60kW up to 1000V battery.
I'm not completely sure this works off-grid but I think so.
If 18kW from battery, 33kW starting surge, 36kW from PV was sufficient, I would use Sunny Island.
Up to 500 kWh battery (per 3-phase cluster.)