Help With REVO II VE 5.5kw - CT Function

As English forum, your Google translate might show everything in German.

For the non German speaking people on the forum:


I thought you were German ?
Only have 6 panels and the open circuit voltage is about over 40v
Revo starts working from as little as 120v and up to 450v max.
It worked and then I tried to pair with Victron Multiplus in parallel and since then Revo Inventory doesn't want PV anymore

6 panels, 216v. As it starts from 120v, not a big problem.

Victron Multiplus.
In parallel...
Oeps...

You are aware that 50hz (or 60hz) AC isn't synchronized??
That's why there are parallel kits for the Revo units? To let them talk to eachother?
One is master and "gives the beat" the other(s) are slave and follow that lead.

You probably are lucky you didn't fry both inverters totally.

How is the Victron?
Still working?
And the inverter part of the Revo?

I hope still working also.

I see 3 different solutions:
(If both inverters are still working)

1. Buy SmartSolar MPPT 250/70 or 250/100 (about €750)
And use both Inverters as just inverters, no parallel (!!)

2. Buy new Revo (also about €750) and parallel with the older unit.
Use this MPPT.

3. Try to fix the defective unit.
It was "abused" in almost the most horrible way.
I don't think the MPPT is fried.
The AC got a "beating"

Probably the AC to 48v board
Screenshot_20220425_195237.jpg

(I guess your inverter has similar)
Or worse... The whole mainboard.

I have some (used) spare parts (long Story) better ask Sorotec first.

Transport from Thailand is about €35 -50 depending on method

Alternative (cheapest solution) is wire the panels as 2x3, and buy PowMr MPPT.
Amazing quality for amazingly low price.
Only their fan makes horrible noise.
(AliExpress is your friend)

That way it's "fixed" for about €75-100.

Parallel 2 different brands of inverters is a "no go"....

One of the first Revo II didn't have sensor, and accently 2 master setting made a whole lot of magic smoke....
(So I have some spare parts)
As I was the first, and Sorotec found it was partly their mistake to make this error possible, I received replacement parts.

Still paid a few hundred $$ for import fees... That's Thailand :)
 
As English forum, your Google translate might show everything in German.

For the non German speaking people on the forum:


I thought you were German ?
Only have 6 panels and the open circuit voltage is about over 40v
Revo starts working from as little as 120v and up to 450v max.
It worked and then I tried to pair with Victron Multiplus in parallel and since then Revo Inventory doesn't want PV anymore

6 panels, 216v. As it starts from 120v, not a big problem.

Victron Multiplus.
In parallel...
Oeps...

You are aware that 50hz (or 60hz) AC isn't synchronized??
That's why there are parallel kits for the Revo units? To let them talk to eachother?
One is master and "gives the beat" the other(s) are slave and follow that lead.

You probably are lucky you didn't fry both inverters totally.

How is the Victron?
Still working?
Und der Wechselrichterteil des Revo?

Ich hoffe, es funktioniert auch noch.

Ich sehe 3 verschiedene Lösungen:
(Falls beide Wechselrichter noch funktionieren)

1. SmartSolar MPPT 250/70 oder 250/100 kaufen (ca. 750 €)
Und verwenden Sie beide Wechselrichter als reine Wechselrichter, keine parallelen (!!)

2. Neuen Revo kaufen (ebenfalls ca. 750€) und parallel zum älteren Gerät.
Verwenden Sie diesen MPPT.

3. Versuchen Sie, das defekte Gerät zu reparieren.
Es wurde auf fast die schrecklichste Weise "missbraucht".
Ich glaube nicht, dass der MPPT gebraten ist.
Der AC bekam eine "Schlage"

Wahrscheinlich die AC-48-V-Platine
View attachment 92525

(Ich denke, Ihr Wechselrichter hat ähnliches)
Oder noch schlimmer... Das ganze Mainboard.

Ich habe einige (gebrauchte) Ersatzteile (lange Geschichte), besser zuerst Sorotec fragen.

Der Transport aus Thailand kostet je nach Methode etwa 35-50 €

Alternative (billigste Lösung) ist, die Panels als 2x3 zu verdrahten und PowMr MPPT zu kaufen.
Erstaunliche Qualität zu einem erstaunlich günstigen Preis.
Nur ihr Lüfter macht fürchterliche Geräusche.
(AliExpress ist dein Freund)

So ist es "fixiert" für ca. 75-100 €.

Parallel 2 Wechselrichter unterschiedlicher Marken ist ein "no go"....

Einer der ersten Revo II hatte keinen Sensor, und die akzentuierte 2-Master-Einstellung machte eine ganze Menge magischen Rauch ....
(So habe ich einige Ersatzteile)
Da ich der erste war und Sorotec feststellte, dass es teilweise ihr Fehler war, diesen Fehler zu ermöglichen, erhielt ich Ersatzteile.

Immer noch ein paar hundert $$ für Importgebühren bezahlt ... Das ist Thailand:)
 
Bei mir ist alles auf deutsch ?
Das wird mein Problem sein.
Habe sterben beide drehte abgeklemmt und PV Spannung ist da und Display geht auch AN.
Was schlagen sie vor...wo kann das Wandler am schnellsten und günstigsten besorgen.
Übrigen Victron MP2 funktioniert weiter ohne probleme
 

Attachments

  • 16508942596913583344460560055041.jpg
    16508942596913583344460560055041.jpg
    188.1 KB · Views: 14
Bei mir ist alles auf deutsch?
Das wird mein Problem sein.
Habe sterben beide drehte abgeklemmt und PV Spannung ist da und Display geht auch AN.
Was schlagen sie vor...wo kann das Wandler am schnellsten und eleganten besorgen.
Übrigens Victron MP2 funktioniert weiter ohne Probleme
Habe zwischen beiden drehen 0,0 Ohm ? Also kein Wiederstand
Im Display wird such modus(boot) angezeigt
 
Everything is in German for me ?
That will be my problem
I disconnected the two and the PV voltage is there and the display is also ON
What do you suggest... where can you get the converter the fastest and cheapest
The rest of the Victron MP2 continues to work without problems

Yeah, Google translate makes everything German for you.

Please do reply in English or I am not able to help you.

I can send you some spare parts, that will take about 10-14 days to arrive.
I can not guarantee it will work.

That is the cheapest, probably fastest.
But... They are Revo II parts.

Alternative:
Contact Sorotec.
21 days, 30? About €250-350

If you have the Victron inverters, don't mix them with Sorotec.

If it's just the MPPT, get PowMR.
If you need Victron quality...
The victron MPPT.

If you need a fast working system with warranty?
Buy new Revo and do not parallel them again :)

My suggestion depending on what you need:
Only MPPT, Victron.
Mppt and inverter, new Revo.
Or, if you can afford it, a victron system.
That will be compatible with the rest of the Victron system.

Not the cheapest solution but for stability, the best.
(And fastest)

PM me if you like me to send spare parts, transport cost can be via PayPal, or Sepa bank transfer (I have Dutch bank account)
 
Bei mir ist alles auf Deutsch?
Das wird mein Problem sein
Ich habe die beiden getrennt und die PV-Spannung ist da und das Display ist auch eingeschaltet
Was schlagen Sie vor... wo bekommt man den Konverter am schnellsten und günstigsten
Der Rest des Victron MP2 funktioniert weiterhin ohne Probleme

Ja, Google Translate macht alles für dich auf Deutsch.

Bitte antworten Sie auf Englisch, sonst kann ich Ihnen nicht helfen.

Ich kann Ihnen einige Ersatzteile schicken, die etwa 10-14 Tage dauern, bis sie ankommen.
Ich kann nicht garantieren, dass es funktioniert.

Das ist am billigsten, wahrscheinlich am schnellsten.
Aber ... Es sind Revo II-Teile.

Alternative:
Wenden Sie sich an Sorotec.
21 Tage, 30? Etwa 250-350 €

Wenn Sie die Victron-Wechselrichter haben, mischen Sie sie nicht mit Sorotec.

Wenn es nur der MPPT ist, holen Sie sich PowMR .
Wenn Sie Victron-Qualität brauchen...
Der Victron-MPPT.

Benötigen Sie ein schnell arbeitendes System mit Garantie?
Kaufen Sie neue Revo und parallelisieren Sie sie nicht erneut:)

Mein Vorschlag je nach Bedarf:
Nur MPPT, Victron.
Mppt und Inverter, neuer Revo.
Oder, wenn Sie es sich leisten können, ein Victron-System.
Das wird mit dem Rest des Victron-Systems kompatibel sein.

Nicht die billigste Lösung, aber für die Stabilität die beste.
(Und am schnellsten)

PM an mich, wenn Sie möchten, dass ich Ersatzteile schicke, die Transportkosten können per PayPal oder Sepa-Banküberweisung erfolgen (ich habe ein niederländisches Bankkonto)
 
PN ist raus
 

Attachments

  • IMG_20220425_175824.jpg
    IMG_20220425_175824.jpg
    76.9 KB · Views: 30
  • IMG_20220425_175805.jpg
    IMG_20220425_175805.jpg
    220.9 KB · Views: 29
  • IMG_20220425_174348.jpg
    IMG_20220425_174348.jpg
    270.4 KB · Views: 30
Hi, guys,

I'm a new solar guy, just installed 4Kw solar PV ( 9*455W panels ) and a REVO II VE 5.5KW inverter. Did it all alone and everything is working. About the REVO II I'm a little disappointed because some functions don't work properly and others the software lies to me.

I'm grid connected and i don't want to inject power to the grid ( also I'm not allowed to because this inverter doesn't have the necessary certification to be feed power to Portuguese grid.)

Fact one - When you don't select on-grid, with CT function off, the screen shows you are not injecting power, but that is a big lie. If you are producing 2000W on the PV and you are consuming 200W ate home, the excess power is going to the grid. It shows zero feed-in but i have measured and it is going to the grid. So that is a huge lie from the brand and from the inverter info displayed. If you select CT, even if you don't have one, it will show you that power going to the grid.

Question one - I have the CT sensor, a 100A/0,333V split core CT and i select the CT on the inverter, deselect on grid mode as said by the Sorotec, but I'm still feeding allot of power to the grid. It seams that bellow the 1000W PV i see the solar panels shutting down and slowly going back up, for some time, like it was trying to limit, but it never stays fixed to the amount I'm consuming at home. After 1000W it doesn't do anything, just sends all the excess to the grid.
Does anyone here have the same inverter with the CT function limiting properly?

I have seen other inverters and when they are limiting and just stay in line with the amount of power produced, 10 to 15W difference but they keep up and never inject power to the grid. This one is not working like that and i don't know if this is normal for this inverter or not.

My settings are:

Mode - PV+AC with CT sensor selected
Ongrid ( not selected )
PV - 4000W
CT Funtion - fine tuned to match power consumptions and injection ( i think it is at 950 )

The screen show CT in + power when injecting and negative when it is consuming.

I appreciate you help guys. Im going mad with this.View attachment 43206
Hey. I have the same problem. Did u figure out the solution. I don't have batteries. Thank u
 