I never found any use for the SOL setting myself. SBU is my choice since Uti would make the unit more of an emergency backup instead of running on PV and battery. Your 28.8v (setting #9) might be a bit high. The default is 28.4 if LiFePO4 battery type LF08 is selected in Setting #8. Occasionally a new LiFePO4 battery will be unbalanced and cause high DC bus voltage spikes as the BMS trips on a runner cell. If you find this happening drop your voltage down to 28.2v or 28.0v and see if that gets you by. Eventually the battery will balance and you can kick it back up but not really needed since the difference in 99% charged and 100% charged is rather meaningless.
You should have a setting #36 that is not mentioned in your manual. This is maximum PV amperage. Unless you need to limit how much your battery is getting from your array I would set it and the Max charge amperage setting #7 at the 80 amps.
24.6v for transfer to Main should work. I run mine at 24.0v and back to inverter at 26.8v Be aware that the low voltage alarm #14 must be set .2 volts higher than transfer #4 or it will alter the transfer voltage to that. Also #35 affects #5
ETA: BTW you can peel off the plastic display panel shipping protector with the little black tab on it.
You should have a setting #36 that is not mentioned in your manual. This is maximum PV amperage. Unless you need to limit how much your battery is getting from your array I would set it and the Max charge amperage setting #7 at the 80 amps.
24.6v for transfer to Main should work. I run mine at 24.0v and back to inverter at 26.8v Be aware that the low voltage alarm #14 must be set .2 volts higher than transfer #4 or it will alter the transfer voltage to that. Also #35 affects #5
ETA: BTW you can peel off the plastic display panel shipping protector with the little black tab on it.