Thank you for your answers.
Here is what I have for now. I have two EG4 48/100 500v mppt charge controllers says max is 22 amps. and 1 tracker per controller
On each charge controller I was hoping to have 7 series 2 parallel (total of 14panels) these have a Isc of10.19 voc of48.74 and rated at 395 watts.
But unfortunately those panels are out of stock and might be unavailable.
The replacements I am looking at are 455 watt 49.35 Voc and a Isc 11.44
This is severe over paneling of these SCC's. Input rating is 5500W. I caution pushing these SCC's to limits. One member here stated his unit failed but when I pressed him for information on his PV, he never responded. I'm pretty certain he severely over paneled the unit or some cold day the VOC went over.
I have a pair installed with 16 530W panels, I run 8S per unit, VOC is 49V, ISC is around 13A. I have seen as much as 5100W for extended periods run thru the MPPT on partly cloudy days. These seem to take the watts available from PV, very efficient unit. I will be releasing a video someday on my PV and have some footage of the SCC pulling more watts on a string than the panels are rated for.
In your case, I would purchase another SCC, use 9S without any parallel strings on a unit. This gets you to 27 panels and you get full output of available PV yield. For $400 per SCC, that really is a no brainer. Keep the volts high and amps low is way more efficient. 3 units spread the heat produced and the higher voltage lets the MPPT run cooler. Higher amps create heat, heat causes failures in electronics.
You will need to look at max VOC at your coldest temps for your area and determine if VOC at 9S will go over the 500V rating of these units. I suggest the Midnite calculator.
https://www.midnitesolar.com/sizingTool/
I have space considerations because these are mounting to the top of a few shipping containers. The length of the panel has to be very close to 80 inches which limits my choices.
If I use them the Isc of the parallel strings would be 22.88 amps or almost a full amp more than the max on the spec sheet.
If you could explain why or why not this is or is not a deal breaker I'd be grateful, I do need to know if it will work or if I am going to shortly have to replace the charge controllers because I went too far out of the spec.
If you want to over panel, clipping will occur and you lose that potential yield. As to whether these units are prone to failure with severe over paneling is undetermined at this point. It would have been helpful if the member with the failure had listed the PV input but some people sometimes realize their mistake and don't want to look bad in public.
If you do over panel and have a failure, please share the information, it helps anyone looking at the SCC's to determine if it fits their system.
One more thing is these units have a firmware update to correct the F01 code from setting. I did a video showing how to update firmware on these and the cable needed.
https://diysolarforum.com/threads/e...-mppt100-48hv-sets-code-f01.68669/post-889561 If you do not have the RS485 to USB custom cable needed, contact EG4 and they will send the cable out free of charge.